This thread sort of follows on from a previous of last week regarding boiler locks on the domestic hot water (which I have now resolved by heating water in the morning for 30mins and again in the afternoon). This time I have established that boiler anti-cycling are occurring on the central heating as well.
The chart attached shows exactly what is happening.
So I have a 1 year old Valliant ecoTEC Plus 428 which once the system has completed a heating burn of say 1 hours duration, the room thermostat then shut off for say 15 minutes, then calls again for heat again, the boiler ignites and completes its purge checks and during this process shuts down due to the boiler temperature being very close to the set Flow Temperature.
These are the system characteristics that I know:
D0 set to 20KW
Pump over run set to 5 minutes
Anti-cycling set to 20 minutes
Flow temp set to 45 C
18 radiators on the system equivalent to 24KW
Yonos Pico 25/1-8 pump running at 40 Watts equivalent to 4.5 m head
House is 15 years old
Floor area 300sqm
Heating bill per year 24000KW
Don’t know the heating loss of the building.
There is a bypass valve that is fitted and is set to 0.3
All other boiler settings as factory set.
I have learnt from the thread of last week that reducing d0 is not going to help, as the boiler completes its purge checks on high power, and d0 does not adjust the power during the purge checking phase.
My limited assessment is that the boiler fires up and gets up to temperature, shuts down and flows the water around the bypass circuit and if this time is only 15 minutes the water is still quite hot, boiler fires up again and the water very quickly gets close to the set flow temperature and then shuts down. You can see from the second burn cycle that once some cooler water from the central heating system has flowed through the boiler it’s a lot cooler and will start up normally.
I have tried to provide all of the information that I can. Any recommendations as to what I should try?
The chart attached shows exactly what is happening.
So I have a 1 year old Valliant ecoTEC Plus 428 which once the system has completed a heating burn of say 1 hours duration, the room thermostat then shut off for say 15 minutes, then calls again for heat again, the boiler ignites and completes its purge checks and during this process shuts down due to the boiler temperature being very close to the set Flow Temperature.
These are the system characteristics that I know:
D0 set to 20KW
Pump over run set to 5 minutes
Anti-cycling set to 20 minutes
Flow temp set to 45 C
18 radiators on the system equivalent to 24KW
Yonos Pico 25/1-8 pump running at 40 Watts equivalent to 4.5 m head
House is 15 years old
Floor area 300sqm
Heating bill per year 24000KW
Don’t know the heating loss of the building.
There is a bypass valve that is fitted and is set to 0.3
All other boiler settings as factory set.
I have learnt from the thread of last week that reducing d0 is not going to help, as the boiler completes its purge checks on high power, and d0 does not adjust the power during the purge checking phase.
My limited assessment is that the boiler fires up and gets up to temperature, shuts down and flows the water around the bypass circuit and if this time is only 15 minutes the water is still quite hot, boiler fires up again and the water very quickly gets close to the set flow temperature and then shuts down. You can see from the second burn cycle that once some cooler water from the central heating system has flowed through the boiler it’s a lot cooler and will start up normally.
I have tried to provide all of the information that I can. Any recommendations as to what I should try?