thanks. as part of this test, do I also need to send a live to the relevant terminal on the cylinder demand terminal box? am I correct to assume that is there to tell the modulation logic to stay out of the way, and thus makes the difference between the boiler running in CH-mode, cool and efficient, and DHW mode, hot and full-power? I haven't had the lid off yet, will do so , however I very much expect this terminal box is not connected
Right, you turn off the power, disconnect the Viessmann interface box from the boiler. You link the Switched L to the Permanent L in the right hand part of the boiler control box.
You then select HEATING OFF on Evohome, pin the motorised valve over to hot water, and reinstate the boiler power.
The boiler will then treat the demand as normal with no OT involvement. Assuming (as I do, because we've fitted lots of WB1Bs) this works and you get 75C, throw away the Viessmann interface box and the Evo OT relay, and use on/off BDR91s with your Evohome instead.
I'm intrigued whose idea it was to create a system with this particular mix of hardware. Was it you or the installer?