Can you upload some photo and/or a diagram of the cylinder set up. When the kitchen tap was fitted and the cold mains supply turned off, opening taps should not have drained the cylinder. It should have just depressurised and settled somewhere near the top when the hot taps were opened. Did the balanced cold taps continue to run when this was done and did the water from them become hot? In effect, did back syphoning occur thus pulling water out of the tank, via the cold inlet?
For hot water (very hot water even) to come out of the cold taps, means that the pressure from the cylinder is overcoming the incoming mains pressure and that sounds like a fault with the inlet control group/balancing valve.
Hi dilalio, thanks for the ongoing input.
Not sure how to post diagrams but if you refer back to page 11 of the link I put in at post #18 on page 2 of this thread you will see how it should be if it was installed today.
My installation is exactly the same except for the fact that my 8 bar PRV is part of the incoming cold water control group to the right of it (before the tee to the balanced cold) and not at the cylinder inlet with a second check valve next to it (after the tee to the balanced cold). My only check valve is in the inlet control group, so where this stops expanded water getting to the drinking water downstairs, it doesn't stop it getting to the balanced cold.
This was acceptable at the time of installation and up until now has only resulted in a few seconds of warm water at the bathroom taps before they run cold. Even then it was only on occasions and a barely noticeable minor nuisance. Megaflo put it down to an installation design fault and more of an inconvenience than a major problem.
Now, clearly something has changed and I do have a major problem as I get water at nearly 60 degrees coming from the cold taps. My reasoning is that when the hot water was partially drained from the tank (cold mains off... hot taps on...cold taps off) it essentially re-charged the air gap. In any case I have re-charged the air gap properly on Friday.
So what has gone wrong? I can only think that the floating baffle has got stuck and doesn't rise and fall fully any more and that as a result the pressure builds up in the tank as the water tries to expand. It could potentially reach just under 8 bar and so not show a discharge through the tundish but obviously would be a good few bar higher than the 3 bar maximum cold inlet. This would then cause the backflow through to the balanced cold.
I have felt the pipes in the airing cupboard so I'm as confident as I can be as an amateur that things are happening as I've explained. I just have no way of seeing inside the tank so cannot prove my theory is 100% correct.
As to a solution, well I guess a new Megaflo is out of the question hence I want to know if an external expansion vessel could be installed in the hot water outlet of the tank. Even if the floating baffle is working, or partially working, I can't see that an external expansion vessel could do any harm. Surely the at worst it could only make no difference.
If it did make no difference then that's the point at which I feel I should move the 8 bar PRV to where it is in the diagram I've referred you to and put a check valve between it and the balanced cold water tee piece.
An external expansion vessel
and moving the PRV/fitting another check valve would definitely fix the problem and bring the system up to date as far as I can see but I need some opinions as to whether I'm right before I head down that road. Then there's the issue of the length of the discharge pipes from the PRVs to the tundish that I mentioned earlier. That could throw a spanner in the works.
I've explained as best I can I'm afraid. What are your thoughts?