And what makes a 6mm² trickier than a 4mm²?
How many accessories can accommodate 2 x 6mm cables?
And what makes a 6mm² trickier than a 4mm²?
Well, many/most BS1363 accessories (e.g MK sockets and FCUs) claim to have a terminal capacity of 2 x 6mm².How many accessories can accommodate 2 x 6mm cables?
Well, many/most BS1363 accessories (e.g MK sockets and FCUs) claim to have a terminal capacity of 2 x 6mm².
However, more to the point, if 6mm² cable is being used for good reason, the accessories to which it is likely top be connected (e.g. 45/50A switches, cooker connection units and 'connection plates etc.) will usually have a claimed capacity of at least 3 x 6mm².
I've never knowingly used one.How many accessories can accommodate 2 x 6mm cables?
Have you never knowingly used, say, an MK 13A socket or FCU ? ...I've never knowingly used one.How many accessories can accommodate 2 x 6mm cables?
Exactly what hairs do you believe have been split?Here you go again Mr Splitting Hairs
You didn't actually. You asked the question (which may have been intended as rhetorical) ....I said not many accessories will accept 2 x 6 mm cables
...and I answered that question, indicating that many of the accessories we use every day (probably most accessories we use every day, other than those on lighting circuits) claim to have a terminal capacity of 2 x 6mm² or greater.How many accessories can accommodate 2 x 6mm cables?
How big was the load on this 32A circuit. Per BS7671, 2.5mm² flex has a maximum CCC of 25A.This is what a 2.5mm² flex looks like having powered a catering wagon from a 5.5KVa genset or 32A MCB
My apologies, I edited too much off.Have you never knowingly used, say, an MK 13A socket or FCU ? ...
View attachment 328172
Kind Regards, John
I did measure But I don't recall, however it was protected by a 32A MCB at that time (Not that cable though) so theoretically only 25ish% overload possibleHow big was the load on this 32A circuit. Per BS7671, 2.5mm² flex has a maximum CCC of 25A.
Kind Regards,John
That's a lot better Now we are totally agreed!My apologies, I edited too much off. .... I have never had a problem fitting 2x6mm² into any 13A or 15A socket.
Fair enough. Strictly speaking,of course, 2,5mm² flex is not adequately protected by a 32A MCB.I did measure But I don't recall, however it was protected by a 32A MCB at that time (Not that cable though) so theoretically only 25ish% overload possible
Well I must plead guilty.True. What about US Amps ?
...and I answered that question, indicating that many of the accessories we use every day (probably most accessories we use every day, other than those on lighting circuits) claim to have a terminal capacity of 2 x 6mm² or greater.
That would be the "centipound""1 New Penny"