That's all true. However, although it's allegedly the main reason that ring finals came into existence, 'amount of copper used' (or even the cost of it) would not be a significant criteria in my melting pot when I was making a ring/radial decision.But for many installations, I think you'll find that a 32A radial using 4mm cable uses more copper than a 32A RFC using 2.5mm cable. It does depend on the topology, but in most houses, to "close the ring" doesn't actually need all that much extra cable. Since 4mm cable has 60% more copper than 2.5mm, that means you can add nearly 2/3 of the radial length to complete the ring before you are using more copper in the (2.5mm) RFC than in the (4mm) radial. In most houses, it would be difficult to exceed that with a sensible cable route.
I also used to be 'frightened' of 4mm² cable for that reason but, as I've acquired experience, I don't really find it much worse than 2.5mm², in most situations, any more.Not to mention, it's hard enough terminating multiple 2.5mm cables in some of the socket/backbox combinations - 4mm can't be easier
Kind Regards, John