I washing machine (not washer/drier) and dishwasher have their heating elements running for a relatively short time, the drier however be it standalone or built into the washing machine where it uses resistive heating runs for quite a long time in comparison, so the appendix 15 of BS 7671 where it says
The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable (Regulation 433.1.5 refers). This can generally be achieved by:
(i) locating socket-outlets to provide reasonable sharing of the load around the ring
(ii) not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit
(iii) connecting cookers, ovens and hobs with a rated power exceeding 2 kW on their own dedicated radial circuit

(iv) taking account of the total floor area being served. (Historically, limit of 100 m² has been adopted.)
Likely the drier unless a heat pump type should be on its own dedicated circuit, however the stand alone washer and the dish washer although likely over the 18 kg where without wheels is considered fixed equipment not portable so following the advice to the letter should have a dedicated radial circuit, in the real world the load is for such a short time, it is unlikely to cause a problem.

Also traditionally the washing machine would has a switch local to it, so it can be switched off without touching the washing machine. Grid switches like this 1712998090635.png often together with freezer etc, were common practice, in the main as washing machine weights have been known to come loose, and the machine could wreck a kitchen, where one can't get near it to turn it off, today washing machines tend to have a built in sensor so if the load is not even distributed it will auto switch off, so there is no longer the same NEED to fit one, however still common to fit them to supply any socket outlet hidden behind equipment so equipment can be isolated without pulling it out first.

So it is the drier which is the problem, be it built into the washer or stand alone, where it uses a resistive element, the heat pump drier, and the washing machines both for clothes and dishes are not really a problem as the heating element is used for such a short time.

On a 40ºC setting the washing machine in my sons narrow boat in spite of being rated at 2.3 kW would not trip a 6 amp B type MCB, it would trip a 4 amp, but not a 6 amp. It did not use the heating element for long enough.

As to water ingress this is unlikely, and would cause all sorts of other problems as well like a wet floor, and the RCD built into the modern consumer unit (Fuse Box) means should it happen it will likely fail safe.

So big question has to be, washing machine or washer/drier as this does change what is required. I note you can buy a duel inverter heat pump 9 kg washer drier, but at £750 they are not common as yet. However the heat pump drier is not cheap either, starting at around £400, as to if worth using a heat pump drier not so sure.

I had a resistive vented drier with a option of 1 or 2 kW and since the option was at back of machine, it was always set to 1 kW, it would run for 90 minutes, and some times the clothes were not dry, no built in sensor, so would be put on for a further ½ hour. The replacement heat pump drier uses around 600 watt, it does have a sensor, and runs for around 2½ hour for most loads, some do take longer.

So in real terms yes the heat pump does use less, but not that much less, it is hard to measure power use as it will start to turn the heat pump on/off with a mark/space ratio near the end of a long drying cycle, so I would estimate it uses around two thirds of the power used by the resistive type. But that is a lot less of a saving to what the reports say.

As to washer/drier, they clearly as built some 10 years ago wasteful in their use of water, as they used the cold water to cool the condenser, unlike the stand alone drier which used the ambient air in the room to cool the condenser heat exchanger, as to which is best not sure, as with a small room the room gets too hot, reducing efficiency.

However I digress, the point is power used, and so with a drier we have three common power use, 600 watt heat pump, and 1000 or 2000 watt with resistive, at 1000 watt no problem really, but although my drier had the option 1000 watt or 2000 watt, my washer/drier has no such option, you get what you get, and to be frank the washer/drier seems to get very hot, not sure it does the clothes much good. (I have a washing machine and heat pump tumble drier in centre floor, and washer drier in the lower floor so have both) I will happily leave the heat pump drier running unattended, but not the washer/drier too many pictures like this 1713000718965.png which I assume is a washer/drier as it looks like a concrete weight on the top, and stand alone driers don't have weights.
 
Sponsored Links
The switch needs to be accessible and visible (otherwise it may as well not be there), so above the worktop and not hidden in a cupboard or behind the machine. Especially if somebody one day fits an integrated appliance. You will be needing plenty of outlets and switches above the worktop, so plot them all in a row about 150mm above.

The socket can then be behind the machine if you want. If the machine needs to be removed for maintenance it can be pulled out to the extent of the flex. It is easier and quicker to remove if you have a plug and socket rather than hardwired.

But dishwashers in particular are 600mm deep and usually have no gap to allow the projection of a plug, so it is better not to have the socket directly behind.

I agree with not having the electrics under the sink or taps. One day there will be a leak or overflow.
 
Thanks all
Also when I select installation wirh delivery for the dishwasher, how do I know if I need to get a plumber to do something first to the pipe work as the people before never had a dishwasher.
 
The socket can then be behind the machine if you want. If the machine needs to be removed for maintenance it can be pulled out to the extent of the flex. It is easier and quicker to remove if you have a plug and socket rather than hardwired.
Noooooo. You obviously haven't been to houses to do PAT testing!
An empty washing machine weighs a ton. Two ton if it is full of wet washing (it always is). Plug and socket in an accessible position, have a thought!
 
Sponsored Links
The socket for the washer could go beneath the draining board, I can't see a problem. Personally I hate it when sockets and waste pipes are left directly behind appliances. I always go the the side, which usually involves cutting a couple of holes in the sides and backs of the units.
 
An empty washing machine weighs a ton. Two ton if it is full of wet washing (it always is)
Is something that weighs a ton or two classed as a 'portable' electric appliance? What if an appliance such as a washing machine, dishwasher, oven etc is hardwired to an outlet?
 
Is something that weighs a ton or two classed as a 'portable' electric appliance? What if an appliance such as a washing machine, dishwasher, oven etc is hardwired to an outlet?
PAT is a misleading term, from memory it should be "In service equipment", meaning everything hard wired or plugged in
 
A Pat testing company will insist on Pat testing everything at four quid a pop. Many of those things do not require testing though as they either do not come under the heading of portable or they are double insulated.
 
Is it a portable appliance?
Mate, when you are working for letting agencies, they have alist of the appliances etc that they provide to the tenant. They want everything tested to cover their backs. They dont care if an item is, or is not, included in the Code of Practice (incidentally the COP was revised after that Parker-Bell document was produced) they want EVERYTHING tested.
 
Mate, when you are working for letting agencies, they have alist of the appliances etc that they provide to the tenant. They want everything tested to cover their backs. They dont care if an item is, or is not, included in the Code of Practice (incidentally the COP was revised after that Parker-Bell document was produced) they want EVERYTHING tested.
Indeed, I used to test a couple of factories, lots of presses, sewing machines, "test everything" was the remit, apart from the telephone switchboard

 
Indeed, I used to test a couple of factories, lots of presses, sewing machines, "test everything" was the remit, apart from the telephone switchboard
When I left school, I was a telephone apprentice. In the exchange where I was based was a very large manual switchboard.
I did try and test some of the operators!
 
A Pat testing company will insist on Pat testing everything at four quid a pop. Many of those things do not require testing though as they either do not come under the heading of portable or they are double insulated.
Surely the test inventory is down to the duty holder, if i was told not to test an item , I made sure it was noted on the report. It was a good day when my tester went pop and ended up in the skip
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top