Afaict phase-neutral fault current will usually be higher than phase-earth fault current because earth wiring is usually higher resistance than neutral wiring but there are a couple of scenarios where PEFC could be higher.
1: A bad neutral connection.
2: An installation with significant parallel earth paths (supplementary bonded structural steelwork, conduit/trunking systems, systems where several submains run parallel to each other and have their earths linked at the far end) .
This to me is the problem. Using 1.67 is all well and good when twin and earth of the same type is used throughout and there is no bonding to the earth used on the ring.
However to find a house with full plans showing exactly what is connected to what and what cable is used is rare and we get sheds taken from FCU's of the ring with SWA and bonding taken to pipes etc. So to compare the line or neutral impedance to earth impedance just does not work.
To take a socket and really does not matter too much which one and record the readings for that socket when the installation is in good order means in the future one can compare those readings to see quickly if anything has gone wrong.
However having said that I found with my own house the RCD trips when trying to measure the loop impedance on one ring yet does not trip with same make RCD on the other circuit so although theory is OK in practice with my house it's a case of using low ohm meter.
I do however have the readings for kitchen sockets on the ring the loop tester will test and once a year I retest and compare. At home reasonable vibration free never found a fault but at work mainly of things like batching plants I have high lighted faults before they caused a break down by simply measuring and recording the loop impedance.
Metal framed buildings do seem to have more problems than the domestic house with vibration causing terminals to become lose. However it would be hard to blame any one where they have become lose.
I did have one house with a problem with the telephones where another electrician had failed to find the problem. It did seem rather an odd fault so I started to measure the loop impedance. I got some strange readings so went to the consumer unit where I found every screw lose where the MCB's were connected to the bus bar. It would seem the consumer unit supplier had slotted the MCB's requested into place but not tightened the screws and the electrician fitting it had not read the notice saying check all screws for tightness and had wrongly assumed since already fitted all screws would be tight. With that case clearly the electrician was at fault. But cases where one can show something as plane as that are rare.
But again it was the loop impedance readings which alerted me to problem so had these been required on the paper work then it would have also alerted the other electrician to the problem.