Thanks Terry. Please confirm there are 4 in the photos and I'll do it.
Need to see picture of the pipe that's dripping and context of where it comes and goes from / to.
Was the system cold ,no heating had been on for at least an hour before you did the test ?
You need to test for a much longer period ,overnight preferably.
If water loss is through the boiler itself ,and there is no weeping joints in the boiler,it's either coming out the PRV ,or the condensate pipework ( pin holed heat exchanger).
Need to see picture of the pipe that's dripping and context of where it comes and goes from / to.
It is Indicative of a boiler issue ,however it is not conclusive as one of the valves may not fully close (internally) and could mislead us.Thanks Terry. Understood. Guess I can pull the pipe apart to check how long it drips for.
Did the isolated boiler dropping from 1.6 bar to zero not tell us anything?
Yes, I've already tried that. See about 6 posts back.Did you try isolating the boiler?
Can't you disconnect the condensate pipe ,near the boiler where there is a leaking joint ,looks like a black rubber seal ,where the smaller diameter goes into the reducer, does it just push fit in ?