Shows I do listen to what you and others say, as to the boiler, that is a hard question, we are trying to guess why it says things like should be supplied from the same supply?
I wouldn't say that one has to guess. Is it not probably fairly obvious why they are saying that - i.e. because they want there to be a 'single point of isolation' for the ("230V" supply to) the boiler and all associated components of the heating system?
As for "why
it says ...", what is the "it" you are referring to? Perhaps I have missed it, but I can't think of any regulation which actual says what you refer to - rather, it is something which one often reads in MIs for boilers.
Again it is the English "The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any, other Purpose.
(Note the full stop, it seems plumbers choose not to see the full stop, which changes what is said as it continues)
Single-core cables that are Coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3."
I'm not sure what this has got to do with the current discussion, but I don't really get your point, since the two sentences relate to different things.
As you are aware, the usage of conductors can be identified by the colour of their intrinsic insulation ('throughout their length") OR by the colour of over-sleeving at the ends (which 'over-rides the insulation colour). The first sentence says that G./Y can
only ever be used 9as insulation colour or over-sleeving) a protective conductor, but it does
not say that,
in general, a G/Y insulated cable cannot be over-sleeved with some other colour to indicate a use other than as a protective conductor. Hence, as we know, although most of us don't like the idea, it is permitted to over-sleeve a G/Y-insulated conductor in a multiple-conductor cable with, say, brown, to indicate that it vis being used as a live (actually line/phase) conductor.
The second sentence qualifies the first, by saying that, in the specific case of a G/Y-insulated conductor in a single-core cable, it is not permitted to use it as anything other than a protective conductor (i.e. cannot be over-sleeved to identify some other use.
I don't see that the fact that these are two sentences separated by a full-stop is relevant, and I'm not sure in which way you think plumbers may mis-read/misunderstand this reg (by 'not seeing the full stop). Perhaps you can clarify?
I some times think the regulations work against people getting things right. We should say you need to do ABC oh and by the way the work should be registered. Not don't do this work is needs registering as it stops people learning how to do it safely. We all know they will DIY, does not matter how much you tell them they are breaking laws or rules, or assume they are doing it correct, and suggest they ask their inspector what he will accept.
I suspect you really mean 'notification' (or the legislation which requires notification) rather than 'regulations' - for example, people in wales might litter their kitchen floors with extension leads because they don't want to incur the nitrification requirement involved with installing extra sockets OR those who intend to undertake notifiable work without notification may be hesitant to ask for advice about how to do it properly/safely. If so, I agree with you that, in those sort of senses, the requirements for notification (much more in Wales than in England0 may be somewhat counter-productive in terms of safety.
Kind Regards, John