OR - it shows that the 32A circuits (and all the palaver about ring circuits) are not really necessary.
Indeed - as I implied, that may well be true of real-world domestic installations.OR - it shows that the 32A circuits (and all the palaver about ring circuits) are not really necessary.
but the alternative can be very expensive and a waste of our worlds deposits.OR - it shows that the 32A circuits (and all the palaver about ring circuits) are not really necessary.
What 'alternatives' (to 32A circuits) were you considering?but the alternative can be very expensive and a waste of our worlds deposits.
Pah, Portuguese rubbish...Some of us only have 16A radials and 16A outlets.
Multiple 16A radials?What 'alternatives' (to 32A circuits) were you considering?
Kind Regards, John
Well, it only takes two 16A radials to replace one 32A circuit and (assuming Method C) one could presumably use 1.5mm² cable (or, in fact 1.0mm² cable if the regs allowed that for 'power circuits'), rather than the 2.5mm² cable (again, assuming Method C) required for a 32A ring or the 4mm² (yet again assuming Method C) required for a 32A radial - and, not only can the cable be smaller, but the total length of cable needed for the two radial should not really be any greater than one would need for one ring (since one could simply install it using exactly the same route one would use for a ring, but with a bit of cable missing in the middle, actually save a bit of cable).Multiple 16A radials?What 'alternatives' (to 32A circuits) were you considering?but the alternative can be very expensive and a waste of our worlds deposits.
And to prevent that from happening you need to install more circuits.However, for reasons I've explained, I am personally even less keen on the idea of 16A radials than I am of 20A ones, since just a couple of credible loads could easily 'overload' it.
There isn’t a limit. It’s up to the person designing the circuit.Perhaps there should be a limit to the number of sockets per radial. In France I understand each radial is limited to 8 sockets.
Precisely...And to prevent that from happening you need to install more circuits.
So rather than your 32A kitchen ring being replaced with two 16A or 20A radials, you end up replacing it with four or so, one for the washing machine, one for the dishwasher, one for the tumble drier and one for the rest.
I think you've just negated your point of view.Well, it only takes two 16A radials to replace one 32A circuit and (assuming Method C) one could presumably use 1.5mm² cable (or, in fact 1.0mm² cable if the regs allowed that for 'power circuits'), rather than the 2.5mm² cable (again, assuming Method C) required for a 32A ring or the 4mm² (yet again assuming Method C) required for a 32A radial - and, not only can the cable be smaller, but the total length of cable needed for the two radial should not really be any greater than one would need for one ring (since one could simply install it using exactly the same route one would use for a ring, but with a bit of cable missing in the middle, actually save a bit of cable).
Hence, given that the two 16A radials would use a slightly shorter (possibly even 'appreciably shorter') total length of a smaller CSA cable than would be needed for one 32A ring (i.e. less copper), I'm not sure in what sense the two 16A radials (the 'alternative' to a 32A circuit) would "be very expensive and a waste of our worlds deposits". I suppose that must be missing something!
However, for reasons I've explained, I am personally even less keen on the idea of 16A radials than I am of 20A ones, since just a couple of credible loads could easily 'overload' it.
Kind Regards, John
I don't think I've particuarly found faultfinding on rings any more difficult or common than radials.I grew up on ring finals.
In fact, when I first started working as an apprentice, sparks were still installing to the 14th. One guy I worked with used to fit a ring final downstairs and spur off each socket to another one in the corresponding room upstairs.
But 30 years of fault finding horrendous f**k ups on ring finals has put me off them big time!
And the testing procedure for radials is much more straight forward.
I am OK with 20A radials, especially for a "bedroom" floor circuit. Obviously, you need to do your design work, but most properties up to 3/4 beds would be fine with a single 20A radial for such a floor. The IET has written at least one article discussing such design.