I'm in Bournemouth.
Unusual for there to be none on the tails.
Of course, he may not be brilliant and could have clamped the CPC (earth wire) mistakenly thinking that's how it is done.
Did neither of the electricians at least suggest some (more) bonding?
I am remembering that on one test there was five volts between shower and waste yet none between radiator and waste.
Could he have clamped the tails (supply cables) or the light circuit and found there was 'no leakage'?I don't understand that. It may be true that he didn't find any significant voltages in places they shouldn't be - but the way (really the one and only definitive way) to determine whether there are any 'leakages to earth' is to undertake IR tests!It's winding me up to be honest!! The guy left me his number, so I just phoned him, he is saying he doesn't need ot do an IT test because he found no leakage to earth.
Unusual for there to be none on the tails.
Of course, he may not be brilliant and could have clamped the CPC (earth wire) mistakenly thinking that's how it is done.
Did neither of the electricians at least suggest some (more) bonding?
I am remembering that on one test there was five volts between shower and waste yet none between radiator and waste.