Hmmm, so the electrician has been.
He went around the house testing with a multi-function meter, he said that the earth to the house is all fine, he was plugging it into sockets and testing against radiator pipes, then against radiator pipes to the shower, in what appeared to be differing combinations...
Nothing, he said he saw 1v at one point but said he was out of ideas as to what is causing it...
SO, I'm not sure whether to feel reassured or not to be honest, I know what I'm feeling, although nobody else in the house has noticed it (which isn't a huge surprise as they're not as observant as me )!
His only comment was that there didn't appear to be "cross bonding" across all the pipework and that our existing consumer unit is of an old type so it may be wise to replace that with either a split load RCD or an RCBO in line with next years expected regs...
He wondered out loud if it might be intermittent, but no idea how to test that...
It makes me feel like I want a second opinion I think...
2 things.
1) DO NOT USE THE SHOWER
2) What you require is an answer and a fix, not an opinion.
True -provided that there is an answer which relates to something which needs to be fixed.2) What you require is an answer and a fix, not an opinion.
I suppose that doesn't really surprise me.There were some similar threads elsewhere in the recent past and, for whatever reason, none concluded with a reason for the problem nor a solution.
Indeed. In fact, if no explanation/solution can be found, then (even though it shouldn't really be necessary) bonding together everything metallic (within reason!) within each of the affected bathrooms ought to ensure, 'once and for all', that no pds can exist between anything and anything else within any of those rooms.,Presumably, if the shower pipe and metal waste are bonded then there can be no potential difference.
Quite. The plastic waste might have an incredibly high resistance path to earth - but for that to result in a significant pd (albeit capable of resulting in virtually no current) relative to something would require that something to be at a high potential relative to earth - and that seems to be have excluded by the first electrician.With a plastic waste, then what?
Indeed.As this happens in two showers but to only one person who states he can feel varying degrees of tingle depending on the lights supply, I would think it is going to be quite difficult to determine.
One thing that has not been given much attention (probably because we don't like/trust neon screwdrivers) is that we have been told that a neon screwdriver lights up when touched onto any tap in any bathroom (hence probably would when touched onto any of the pipework).Has anyone a likely theory on how this possible?. Don't forget it is not an electric shower.
It should trip, but installing RCDs is not a substitute for locating faults and fixing them properly.If I get RCD's all the way across the board, then at least there is greater protection, and presumably if there is a leak to earth one will trip.
It should trip, but installing RCDs is not a substitute for locating faults and fixing them properly.
Do electricians not carry insulation testers these days?
I have been to a job with similar symptoms to yours. Turned out the floor was live due to a leak from the shower getting into a lighting circuit joint box below the floor.
How far is Southampton from Leeds? I get really frustrated with faults like this and the scores of electricians turning up without a clue about fault finding.
Do electricians not carry insulation testers these days?
I have been to a job with similar symptoms to yours. Turned out the floor was live due to a leak from the shower getting into a lighting circuit joint box below the floor.
How far is Southampton from Leeds? I get really frustrated with faults like this and the scores of electricians turning up without a clue about fault finding.
One thing that has not been given much attention (probably because we don't like/trust neon screwdrivers) is that we have been told that a neon screwdriver lights up when touched onto any tap in any bathroom (hence probably would when touched onto any of the pipework).
Although we don't trust such devices, this seems extremely odd (and something which I have rarely, if ever, encountered) - particularly given the fact that the main problem with these screwdrivers is that they can fail to light up when touched on something live, rather than that they do light up when touched on something which is not live. If one assumes that the electrician has confirmed that all the taps and pipework have an essentially zero pd relative to earth, what the OP describes implies that his body somehow has a fairly high capacitive coupling to L - which seems pretty odd. I suppose that could happen if there were a widespread L/N reversal throughout the installation (which the electrician would hopefully identified) but, apart from that, I would say that this widespread (and, IMO, rather extraordinary) lighting up of a neon screwdriver on taps throughout the house really needs some further thought and investigation, doesn't it?
Kind Regards, John