Maybe you should have asked them why they were making flaky equipment without the necessary protection intrinsic to the device.I used to install a great deal of ADE panels. Their instructions asked for a 2A 1362 in the FCU.
Maybe you should have asked them why they were making flaky equipment without the necessary protection intrinsic to the device.I used to install a great deal of ADE panels. Their instructions asked for a 2A 1362 in the FCU.
I often use 2A vs 3A fuses in sensitive equipment like alarm panels to give a extra margin of safety. Also 0.75mm² flex is rated at 6 Amps; Now say it's got a 5A load applied through it, both 3A and 13A fuses are unsustainable, thus the need for plug top fuses other than 3 and 13 amp.
Ah.I am not in the Trade and [BS 7671] is rather expensive.
THAT
IS
NOT
WHAT
THE
FUSE
IN
THE
FCU
IS
FOR.
I accept .Actually it is 'pedantry'.
I would say that is because of the generally accepted view that, for whatever reason, lighting and lighting circuits are protected by 6A OPDs.... if we really believe the concept that an OPD is there only to protect the cable, regardless of what the cable may be connected to, why is it that virtually everyone here (including myself) regularly advises those who want to run lighting off, say, a 32A-protected circuit circuit that they should install an FCU with a 3A fuse - given that we are usually talking about Method C 1mm² (or even 1.5mm²) cable, for which a 13A fuse would be adequate/appropriate.
All but impossible and it would cause the element to melt.Now assume a metallic object finds its way into the heater and rests across the bare heating element in such a way as to short circuit some of the heating wire, reducing its effective length and hence increasing the current flow. In this hypothetical fault, the current increases to say 13A, the output of the heater is therefore more than tripled due to the fault and the heater's wire glows red hot. Assuming that this doesn't cause the element to burn out, this situation will continue almost indefinitely and could reasonably result in a fire.
Assuming it did happen, why would a hot element cause a fire.In that example, had a lower rating fuse, say a 5A, been fitted it would only allow this overload for a limited time, which would limit the heat build up and may prevent the fire from starting.
That is one reason given sometimes for extractor fans requiring the 3A fuse.In another hypothetical example, a bearing in a 4A appliance fails causing a motor to be overloaded which draws increased current, say 13A which is enough to heat the failed bearing and motor windings to the point of combustion. Again, a 13A fuse will not prevent this overheating, whereas a 5A fuse may prevent a fire.
You say that and it sounds good but are there any examples?However, perhaps as a ‘bonus’ the fuse is also providing a degree of (what should be additional) protection to the appliance itself. Whether this is intentional or not, the protection is still there. In the above scenarios, a suitable but lower rated fuse may, in some specific circumstances have prevented a fire where a 13A fuse may not have done.
Well, there presumably aren't or Europe, America and the rest of the world would be going up in smoke.So I think there are valid engineering reasons why reducing a plug fuse size could at least be considered. As already mentioned,
What do they "recommend" in countries where there are no such things as FCUs?That may be so, but some alarm panels as has been mentioned recommend a 2 Amp fuse in the FCU that is supplying them.
Maybe, but that really begs a similar question/point. If it is felt that a 6A OPD is necessary, that presumably must be because the OPD is being expected to 'protect' something other than just the cable??I would say that is because of the generally accepted view that, for whatever reason, lighting and lighting circuits are protected by 6A OPDs.
I'd certainly say 'virtually impossible' in a 'normal house', wouldn't you?Similarly, I do not like to advise connecting ovens with less than 32A cable but you often say it would be impossible for the short connection not to comply with the fault current requirement.
Yes, but, as in the rest of the thread, I don't think that is a genuine expectation.Maybe, but that really begs a similar question/point. If it is felt that a 6A OPD is necessary, that presumably must be because the OPD is being expected to 'protect' something other than just the cable??
I would, but we can't tell from here.I'd certainly say 'virtually impossible' in a 'normal house', wouldn't you?
Now assume a metallic object finds its way into the heater and rests across the bare heating element in such a way as to short circuit some of the heating wire, reducing its effective length and hence increasing the current flow. In this hypothetical fault, the current increases to say 13A, the output of the heater is therefore more than tripled due to the fault and the heater's wire glows red hot. Assuming that this doesn't cause the element to burn out, this situation will continue almost indefinitely and could reasonably result in a fire.
All but impossible and it would cause the element to melt.
Does the element not get red hot in normal use?
In that example, had a lower rating fuse, say a 5A, been fitted it would only allow this overload for a limited time, which would limit the heat build up and may prevent the fire from starting.
Assuming it did happen, why would a hot element cause a fire.
In another hypothetical example, a bearing in a 4A appliance fails causing a motor to be overloaded which draws increased current, say 13A which is enough to heat the failed bearing and motor windings to the point of combustion. Again, a 13A fuse will not prevent this overheating, whereas a 5A fuse may prevent a fire.
That is one reason given sometimes for extractor fans requiring the 3A fuse.
However, that would be the manufacturer's neglect in designing the product badly.
However, perhaps as a ‘bonus’ the fuse is also providing a degree of (what should be additional) protection to the appliance itself. Whether this is intentional or not, the protection is still there. In the above scenarios, a suitable but lower rated fuse may, in some specific circumstances have prevented a fire where a 13A fuse may not have done.
You say that and it sounds good but are there any examples?
So I think there are valid engineering reasons why reducing a plug fuse size could at least be considered. As already mentioned,
Well, there presumably aren't or Europe, America and the rest of the world would be going up in smoke.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local