My experience of faults is irrelevant. Each appliance has an isolator and does not affect another if a fault. Sounds V good to me. Not expensive either for what it offers.
Reputable makes of RCBOs come in at £20+. Then there's the need for a considerably bigger CU, more cables to be run, more testing to be done.
Gut feel is you'll be looking at getting on for an extra £100 per appliance.
And if you cannot show that your own, or general, experience is that appliance faults are so common that a dedicated circuit for each one is worthwhile then it offers you nothing.
But hey - it's your money and your wall space. If that's what you want, then go for it, but please don't try to insult our intelligence by claiming that it is anything other than a total indulgence on your part.
That is the point single pole with TT is not isolation it is only switching. So let us take a 12 way consumer unit filled with 30 mA RCBO's so in theroy 12 x 30 mA can flow without tripping, yes I know it will never reach that limit but it means 360 mA so to ensure the earth electrode never reaches 50 volt it must have an earth loop impedance of 139Ω. Not the 200Ω considered as the value which if exceeded is unstable. So in real terms we can expect up to 20 volts earth electrode to true earth.
This means the chances of neutral ~ earth faults tripping a RCD are quite high compared with a TN-C-S supply. I would have no hesitation with a TN supply all RCBO and only one single isolator is not a problem. With TT however there is a lot to be said for twin isolators. There is nothing to stop one configuring the board to have two isolators feeding the RCBO's but for extra cost I would say worth while having double pole switching RCBO's even if not double pole sensing for over current.
To me best isolator is a plug and socket. There is no way they can be still connected. There is no need for proving dead you know it is dead.
Do these have to be double pole? One idea is to run a large cable to a small sub CU in a kitchen cupboard and have an MCB for each appliance. This will not be DP of course.
That can, in theory, also happen with TN-C-S. However, in either case I'm not sure that (within reason) the voltage between the installation's 'earth' (i.e. CPCs) and true earth is necessarily all that important, provided that everything is correctly bonded to the MET. The inside of the building can be an "equipotential zone" regardless of what that "equipotential" is relative to true earth.
If risk-aversion becomes as extreme and irrational as to be paranoia, then you would sometimes be right. However, there are a good few perfectly 'sane' people who are, 'rationally', very risk-averse.
If risk-aversion becomes as extreme and irrational as to be paranoia, then you would sometimes be right. However, there are a good few perfectly 'sane' people who are, 'rationally', very risk-averse.
If risk-aversion becomes as extreme and irrational as to be paranoia, then you would sometimes be right. However, there are a good few perfectly 'sane' people who are, 'rationally', very risk-averse.
Do these have to be double pole? One idea is to run a large cable to a small sub CU in a kitchen cupboard and have an MCB for each appliance. This will not be DP of course.
I would have no hesitation with a TN supply all RCBO and only one single isolator is not a problem. With TT however there is a lot to be said for twin isolators. There is nothing to stop one configuring the board to have two isolators feeding the RCBO's but for extra cost I would say worth while having double pole switching RCBO's even if not double pole sensing for over current.
To me best isolator is a plug and socket. There is no way they can be still connected. There is no need for proving dead you know it is dead.
Thanks Eric. Yes, switching and isolation are not the same. A plug & socket is the best isolation, but when appliances are integrated the matter is different. A DP RCBO when off is full isolation and safe to work on the appliance in some way.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local