You beat me to it, John!
and is your duck flying too?
You beat me to it, John!
Ever looked at what the terminals on a BS1363 socket outlet are rated at?The terminals on a 20A switch might only be rated at 20A, but they are on a supply fused at 30A.
You beat me to it, John!
and is your duck flying too?
Fing, I can't see a problem with 20A switches. The 20A rating refers to its switching ability. As Ban has said, 1363 sockets are rated at 13A, but that does not stop us wiring them into 32A circuits. Each outlet is designed to handle a 13A load, just as a 20A switch can handle a 20A load. If you feel better using 32A switches, fine, but myself and many others are confident in our use of 20A switches.
Are they not rated for the full 32A? If they aren't then surely they won't be suitable for use in a 32A radial circuitEver looked at what the terminals on a BS1363 socket outlet are rated at?The terminals on a 20A switch might only be rated at 20A, but they are on a supply fused at 30A.