Don't think it is.The problems occur when people also want to use the armour as equipotential bonding, as is usually far too small for that.
//www.diynot.com/wiki/electrics:swa-earthing#c-pvc-thermoplastic-steel-wire-armoured-cables
Don't think it is.The problems occur when people also want to use the armour as equipotential bonding, as is usually far too small for that.
Don't think it is.The problems occur when people also want to use the armour as equipotential bonding, as is usually far too small for that.
//www.diynot.com/wiki/electric...rmoplastic-steel-wire-armoured-cables[/QUOTE]
Be aware that steel is a lot less conductive than copper!, so you have to compensate for the difference, there is a factor of 8.9 involved
The overall diameter of the bundle of cores is smaller ? ?Its interesting the XLPE cables have less armour CSA. Whats the reason for this?
Possibly. I haven't measured it. ( yet )bernard: So presumably the insulation thickness on XLPE is thinner?
And all the "equivalents" listed in the table were 15 mm or greater so the SWA would appear to be OK for main bonding.On a non pme supply the main earth size can be calculated by using the adiabatic, and then the main bonding can be half the size of the earth, but a minimum size of 6mm.
Adam_151: The factor is nowhere near 8.9.
BAS's link shows the relevant tables from the wiring regs and lists the k values used, the factor is more like 2.25 than 8.9. The figures shown under "Required CSA" already take this factor into account.
In fact the main bonding on a PME system with working RCD will never normally have to carry more than the trip current of the RCD so 6 mm is current and impedance wise a massive over size. It is that size to make it mechanically resilient to damage and then to have a suitably long life time resisting corrosion.
Indeed. We did that topic to death a few months back; as you say, conductance ratios and 'K values' are very different things, and numerically very different. One of the problems in determining the copper:steel conductance ratio is that there is quite a range of conductances for different types of steel, and I don't think that we really know which is appropriate for SWA armour.the regulations state that the minimum copper equivelent CSA of the bonding conductors, and the note below explains this can either be a copper conductor of the tabulated value or of another metal of an appropiate size affording equal *conductance* as the tabulated value of copper CSA. K values do not relate to conductance, they are constants used in the adiabatic which take into account may factors such as conductance, specific heat capacity, permitted temperature rise and are of only for appraising the size of a conductor in relation to fault currents
In fact the main bonding on a non PME system with working RCD will never normally have to carry more than the trip current of the RCD so 6 mm is current and impedance wise a massive over size. It is that size to make it mechanically resilient to damage and then to have a suitably long life time resisting corrosion.
No, infact currents will circulate in the bonding when when the RCD is turned off, and in a network fault a lot more could flow!