Whilst I agree with all that is being said, before people start interpreting too widely, it may be worth reminding ourselves that it only applies to the situation in which one is contemplating using SWA armour for Main Protective Bonding, which I imagine would be a fairly unusual situation. I would have thought that in the majority of situations, one is going to be using armour only as a CPC, in which case an adiabatic calculation (using the 'K factor', which is much smaller than the conductance ratio) is applicable. An exception, of course, would be, say, the supply to an outbuilding which had extraneous-conductive-parts (which needed MPB) - in which case it would, indeed, seem that it would normally be impractical to provide the MPB with SWA armour.Its even worse than that homslaw!
Taking the figure of a 8.9 ratio between steel and copper conductance, that would mean that if you needed a 10mm bond, you need 89mm of armouring to get the same conductance, if you look at the tables for 2C swa you are looking at 95mm before that is acheieved!
Kind Regards, John.