Your subsequent post: ... You cannot or do not 'bond' with CPCs. ... If not connected to an 'earthing system' then the connecting conductors would be just 'bonding' - to equalise any potential.
One might think so but ....
If connected to an earthing system to operate OPDs or RCDs then they would indeed be CPCs.
As I wrote in the last paragraph of my post to which you are responding, even if the bonding conductor were
not connected to the 'earthing' system, it would
still cause an OPD to operate in the even of a Risteard/eric pair of faults (one exposed-c-p having a fault to one live conductor, the other exposed-c-p having a fault to the other live conductor) - so the conductor in question would seemingly be performing the functions of both a bonding conductor and a CPC. I really don't know what I'd call it!
That this earthing system is at a different potential from true earth is, surely, irrelevant.
As I've said, it seems that some people are talking about 'earthing' in that sense - in the absence of any true earth connection. When Risteard, eric or the IET talk about the need for 'earthing' when two Class I items are fed from, say, a local generator, they are perhaps just talking about CPCs connecting to a local, isolated, 'earthing system', which is
not connected to true earth. However, that is usually said in the same breath as 'earth rod', so I'm a bit confused.
You say that it is irrelevant whether the 'earthing system' is at true earth potential, but I think there is an important 'relevance'. If the local earthing system has no connection to (i.e. has a very high impedance to) true earth, then simultaneous contact with one of the supply's live conductors and true earth (e.g. a wet building site) is not dangerous. If the local earthing system is connected to true earth, then such simultaneous contact is potentially dangerous (although it can be mitigated by an RCD).
It cannot be bonded or connected to true earth as that would negate the point of the separated system.
You're talking about an 'isolated supply' (floating w.r.t. true earth), which is what I was also mentioning in the last paragraph. However, I thought we were talking about the pros/cons of
having a connection to true earth, aren't we?
Kind Regards, John