I saw first hand the result when a contractor hit the cable to a housing estate braking only the neutral earth, the three phases were still connected, a radio amateur in the estate had a rather good earth and the guy wiring up his shed (shack) had bonded this wire to the 4 mm earth wire tie raped to the SWA feeding the shed, not a clue why the steel was not used. This 4 mm cable was reduced to balls of copper.
The main problem was he was only one in the estate to have a good earth, had everyone fitted multi earth rods with buried copper tape joining them the current would have been shared, and likely no problem, it was because only one person had the earth that the problem arose.
So if the DNO come and fit earth rods around the estate together within a day of each other then the TN-C-S will become PME and no problem, however if the consumer fits the earth rods they will be fitted over a long time, and until all the estate have fitted earth rods there is a clear danger.
The main problem was he was only one in the estate to have a good earth, had everyone fitted multi earth rods with buried copper tape joining them the current would have been shared, and likely no problem, it was because only one person had the earth that the problem arose.
So if the DNO come and fit earth rods around the estate together within a day of each other then the TN-C-S will become PME and no problem, however if the consumer fits the earth rods they will be fitted over a long time, and until all the estate have fitted earth rods there is a clear danger.