I haven't done many agricultural installations before so does this set up seem ok?
The building is steel framed with a water supply
Pig sty/weighing room is fed from separate building 50mtrs away which has a PME head. The plan is to have a switch fuse feeding an two core swa, then an insulating gland on DB with earth rod (making aTT system) with a 300ma time delayed rcd main switch and 30ma on socket outlets not exceeding 32amp
There is two other pig stys each with there own DB that I will feed with a 30ma rcbo.
Lighting, feed system etc will be protected by the 300ma rcd
Water and steel will both be bonded to the DB
Is the 300ma ok or would a 100ma be better for the little piggies