Yes, I agree with all that, with just the one caveat that usually applies to removal of redundant RCDs - particularly given that it's time-delayed, and therefore shouldn't ever operate, in some situations it can be useful to retain it as a means of isolation.I suppose that need is probably the wrong word to use there but I would definately remove it if I was doing the install.
It serves no purpose as has already been mentioned the OCPD at the origin of the SWA will provide ADS in the event of a fault, and all the RCD does is provide a remote point of failure in the event of a fault.
At least it's time delayed, so it shouldn't ever trip, but I'd still do away with it anyway.
Kind Regards, John.