Lol my mate tried to dig out some discarded re-bar with a mini digger the other week ; bit like David and Goliath- hilarious
Sounds a bit like my house's 'TT' system with a Ze of about 0.25Ω (with bonding in place), despite and earth rod around 70Ω-80Ω when measured in isolation!House now 0.88 ohms. Garage connected with SWA via switched fuse and RCD in house. CPC connected at house and isolated in garage. Armour connected in house and isolated in garage. Plastic box. CPC from new circuit to rod, so garage now TT; couldn't export earth as system continues to second garage. RCD also in garage (I know, but it was acting as isolation switch so left it) New test shows 1.3 ohms on new TT circuit. The ground is wet. Suspect that the PME connections from the local poles are having a good influence. Is this possible?
Again, others may disagree, but it sounds OK to me, provided that everything relevant in the garage is bonded to the garage's TT system (except when you're measuring the earth resitstance!). You already understand that the second RCD is a bit redundant, except as an isolator.- and anything wrong with the layout as described?
Others may disagree, but I personally seriously doubt that the 1.3Ω is down to the rod alone
The best I've seen on a TT was 2 ohms.
It was in a dairy farm, and consists of 3no. 2.4m long rods at various different locations, and a 2m x 20m metallic grid buried in concrete.
That's cheatingThe best I've seen on a TT was 2 ohms. It was in a dairy farm, and consists of 3no. 2.4m long rods at various different locations, and a 2m x 20m metallic grid buried in concrete.
As previously reported, mine is probably 'borrowing' an adjacent property's TN earth, via bonding and the water supply pipe network - Ze 70Ω-80Ω rod alone, down to 0.25Ω with all bonding in place, and still 0.35Ω when all main bonding disconnected (hence only incidental parallel paths to pipework present).I had one 40 ohms then down to six ohms when the water pipe was connected , old lead water main run under a row of terraced houses close to an old pit head.
I think mine was more to do with the ground conditions of the abandoned pit , nearby 100 + ohms is the norm and the whole area is TT.As previously reported, mine is probably 'borrowing' an adjacent property's TN earth, via bonding and the water supply pipe network - Ze 70Ω-80Ω rod alone, down to 0.25Ω with all bonding in place, and still 0.35Ω when all main bonding disconnected (hence only incidental parallel paths to pipework present).I had one 40 ohms then down to six ohms when the water pipe was connected , old lead water main run under a row of terraced houses close to an old pit head.
It's a case of 'what I am allowed to rely upon' (e.g. for earth fault protection) and 'what I've got' being utterly different!
Kind Regards, John.
I'm only speculating about the reason for the very low measured loop impedance via my water supply pipes, but I can't really think of any other very credible explanation for such a low figure.I think mine was more to do with the ground conditions of the abandoned pit , nearby 100 + ohms is the norm and the whole area is TT. The gardens are constanly wet and the houses damp.
What's the lowest anyone has seen with a bog standard single domestic TT rod - 25Ω or so perhaps?
Indeed. I've now found the figures I posted recently:Yes the 10mm2 is the minimum size, I seem to recall we discussed this recently and 6mm2 with a core and the SWA in parallel is greater than 10mm2 copper equivalent, so 10mm2 will be more than adequate
... and that's even without counting the CPC core.Per quick 'back of a fag packet calcs (hope they're right!), for the purpose of the adiabatic equation in BS7671:
- 4mm² 2-core SWA Armour CSA=21mm² Cu equivalent=9.3mm²
6mm² 2-core SWA Armour CSA=24mm² Cu equivalent=10.6mm²
10mm² 2-core SWA Armour CSA=41mm² Cu equivalent=18.2mm²
16mm² 2-core SWA Armour CSA=46mm² Cu equivalent=20.4mm²