I think those figures are a bit out. The ratio of conductance between copper and steel for an equivalent size is about 9:1 so the CU equivalents above will be a lot smaller.
This could be important. Just when I thought I had cracked this one in my recent posts...
...I think that everything I've written in my recent posts remains true in relation to the required CSA of protective conductors in general - indeed, in relation to the requirements for
any protective conductor
other than a main protective bonding conductor with a PME system.
However, in relation to MPB conductors with a PME system, I've just noticed the footnote to Table 54.8 which states that, in that situation, the equivalence to tabulated CSAs for copper conductors should be calculated on the basis of equivalent
conductance, rather than just satisfying adiabatic equivalence in terms of 543.1.
In relation to that one specific situation, I may therefore owe ricicle an apology, and the consequences of this are fairly far-reaching. One has to assume that this footnote has to be taken at face value, and what it means (as ricicle was implying) that, for a MPB with PME, the minimum steel armour CSA which satisfies 543.1 in terms of adiabatic equivalence (i.e. temperature rise under fault conditions) would be pitifully inadequate in terms of satisfying the footnote to Table 54.8. In practice, this means that (particularly if one uses ricicle's 9:1 conductance ratio) unless one is talking about very large SWA sizes (95mm² minimum for 2-core), SWA armour alone is
never going to be adequate as a MPB on a PME system. Of course, if one uses one of the SWA cores (plus armour) as a protective conductor, then 10mm² or larger will be adequate.
Whether the protective conductor going to an outbuilding counts as an MPB conductor is something we could debate, and the answer to that is clearly crucial in terms of non-copper conductor CSA requirements.
I have to wonder whether they really meant that footnote to Table 54.8 to say what it does. There is no mention of length, so a 10mm² copper MPB 500 metres long would theoretically satisfy 544.1.1, per se - which makes one wonder whether they really intended to effectively impose a conductance requirement for non-copper conductors.
Kind Regards, John.