It's a little odd that BS7671 does not explicitly include installation methods for cables in conduit under/within floors.Because it is closest to the cable being installed in a duct under the kitchen floor
As I've just written to Sunray, I don't think we know for certain that it is a concrete floor, nor, if it is, to what extent it is 'insulated' - I would not have thought that it would have thermal insulation both above and below it, which would be essentially what you are assuming by using Method A.
Thermal insulation aside, cable in conduit within masonry (presumably including concrete) would be method B, which would give 2.5mm cable a CCC of 23A.
That is true, but you are then referring to a situation in which the cable itself is totally surrounded by thermal insulation. If cable (or conduit) is buried in concrete, there will be no intervening thermal insulation between the cable (or conduit) and the concrete, so I would imagine that there would be a lot of scope for heat to be transferred to the mass of the concrete, even if there were insulation above or below the concrete.""insulated stud wall cable NOT touching plaster board"" would require 6mm²
The bottom line of all this is that the calculations presented rely on both guesses and some uncertainties in the regs. As a minimum, we should at least obtain clarification of the installation method before attempting any calculations.
I doubt whether the mods would be inclined to expend that much energy in looking in detail at all his posts, particularly if calculations and/or consultation of reference materials were necessary. I think that, as you are illustrating, the forum membership is quite capable of 'policing' these situations satisfactorily, with the added benefit that, if done 'in public', others will soon deal with "incorrect corrections" (which sometimes happen!).Given the number of posts from Winston1 that were somewhere between "unhelpful comment" and "in-accurate advice" it would improve the forum if his postings were vetted before appearing in public. Especially when a dangerous situation could be created if his "in-accurate advice" was taken to be accurate and was used by a DIYer in a project.
Kind Regards, John