I don't think so - or, at least, that's never how I've read the regs. The preamble to points (iv), (v) and (vi) of 701.415.2 says that supplementary bonding may be omitted if there is is "Main Bonding in accordance with 411.3.1.2" (and those other three conditions were satisified) - and I would take that to correspond to your "Main Bonding correctly applied".Does that not come under "Main Bonding correctly applied"?
However, 701.415.2(vi) then goes on to also require that all extraneous-c-ps in the bathroom are 'effectively connected' to that Main Bonding. This will obviously normally be the situation, via the pipework, but I had always taken it to mean that there had to be a demonstrated 'adequately low' (goodness knows!) resistance from the extraneous-c-ps in bathroom to the MPB/MET - i.e. to rule out the possibility of some 'too high resistance' (whatever that means) connections somewhere in the pipework. What did you interpret (vi) as meaning?
Kind Regards, John