From our document
In reference to metallic services we take that clearly to apply to the metallic internal pipework as the services in the street/garden have been plastic for many years
and this, which possible answers a question elsewhere
Generally as far as we are concerned no bonding, no connection
The PME earthing terminal shall not be made available to the customer unless:
11.3.1 A main equipotential bond of not less than the copper equivalent area shown in Table 2 is installed to bond the incoming metallic gas and water services to the customers’ protective conductors; and
11.3.2 Other exposed metalwork in the premises which is directly connected to or in contact with metalwork buried in the ground is also bonded to the PME earth terminal using conductors of size as detailed in Table 2. Note that such bonds are also main equipotential bonds; and that telecommunication cables are exempt from the requirements of this paragraph 11.3.2
In reference to metallic services we take that clearly to apply to the metallic internal pipework as the services in the street/garden have been plastic for many years
and this, which possible answers a question elsewhere
Electricity North West shall not connect or permit the connection of a PME earthing terminal to the customer’s protective conductors, unless satisfied as far as reasonably practicable that the necessary bonding has been made. A contractor’s certificate will normally be required for this purpose.
Generally as far as we are concerned no bonding, no connection