Which is it? Please don't try to pull the wool over people's eyes by claiming it doesn't matter - you might fool some people, but not I, as I know it matters very much indeed.
Perhaps you can explain why you feel that it "matters very much" for a HI ring final circuit to have four paths to earth (CU/MET) from each socket (which I don't think anyone but you believes) whereas two paths (including the situation in which those two paths exist as a single CPC ring) is acceptable for a radial circuit?
My "matters very much" there was about whether the circuit Simon showed was a ring final or a radial, and it matters very much because the requirements are different.
The answer to your question is very simple, and I can give it using the concept of paths if you prefer.
Normally a radial requires a single cpc path. If it breaks then some of the sockets no longer have a cpc, and this is not allowed by the regulations. When moving to HIE, it requires two paths, i.e. twice as many (can be two radial cpcs, or, as you observe, the two paths could be provided by a ring). That improves the integrity, because a break does not leave some sockets without a cpc path. What it leaves is all of the sockets with a cpc which still complies with 543.2.9
Normally a ring final requires a single ring cpc, which as you observe does create two paths for pc current. But to comply with 543.2.9 each socket must always have those two paths because to comply with 543.2.9 you must always install the cpc in the form of a ring. If it breaks then although all of the sockets still have a cpc, they no longer have two paths because the cpc is no longer a ring, and this is not allowed by the regulations.
When moving to HIE, the circuit, just like the radial, requires twice as many paths.
That is a common sense, logical and anomaly free concept to describe as "high integrity".
I think that you are probably "really on your own" on this one, more so than ususal.
I am fully aware of that, but that is because nobody who holds the common belief does so because that is what the regulations
actually say. The believe it because, for some reason, they think they should discount what the regulations
actually say, and instead think they should do something different because they don't (or as this topic shows, will not) accept that the people who wrote the regulations mean what they
actually say.
Let me ask you this - if you asked me to bring you "two individual pieces of rope, each of which is 5m long", and I brought you one piece, 10m long, how impressed would you be with my argument that of course I had complied with your request, because from the POV of the middle of the rope you did have 2 individual 5m pieces, one going this way, the other going that way.
If you can avoid the temptation to derail this by saying "I'd just cut it in half", I suspect you would not think that I had delivered to you the two individual pieces of rope you'd requested.
So why won't you accept what the regulations
actually say?
543.7.1.203(iii) says you need two individual cpcs. Not two individual
paths, two individual
cpcs. Not one cpc with two paths. It says two individual
cpcs.
It also says that each cpc must comply with 543.2.9. Not each path, each
cpc.
543.2.9 contains a requirement for the cpc of a ring final circuit to be in the form of a ring itself. Not the path for protective conductor current, the cpc.
So if you have 1 regulation which says "this circuit needs two individual cpcs", and another which says "cpcs for ring finals must themselves be rings", HOE do you get from there to not accepting that when the circuit in question is a ring you need two individual cpc rings? Particularly when you are quite happy to accept that it does mean two individual radial cpcs when the circuit is a radial?
PS - apologies if I'm behind - I'm sure there are posts made which I've not seen, and not replied to - I will catch up when I can.