The image quality is not sufficient but.....
As has been mentioned it's a carp boiler.
There are two gate valves on the flow/return under the boiler....so there in no protection against overheating....they could easily be turned off by mistake....remove them.
The condensate pipework and flue appear to be poorly supported. Are they terminated correctly?
The expansion vessel will have considerable mass once it's full of water (through lack of regular maintainance). Normallly supported with the feet...is the wall bracket sufficient?
The expansion vessel/safety valve/pressure gauge does not appear to be connected to the boiler pipework ie it's connected to the cold main. There appears to be a stopcock on the pipework from the Cistermiser to the vessel. Is the boiler open vented? Something clearly amiss.
Poor posistioning of pipework above electrics...water ingress risk.
And check there is an auto bypass valve, the flue pipe is high temperature uPVC etc.
Some serious safety issues....turn off until checked out fully.
hi thanks for such a in-depth review
1. crap boiler I agree
2. the gate valves are actually bleed valves (picture unclear)
3. your right, flue has no support at all, condensate is the same (runs into sink waste).
4. I'd have to check the strength of the fixings holding the vessel bracket.. it did appear very strong.
5. old boiler WAS open vented, tanks have been removed and capped.. now sealed.
6. positioning of electrics... very true.. I think its time to call them back.
7. there is no bypass valve, i checked right along to the zone valve. I'll check flue pipe is hi-temp.. I'd imagine this would be printed on it?
thanks for your help.. much appreciated.
mick.