With 230 volt it's not too bad but with 55-0-55 or with three phase 63-0-63 volt systems the volt drop is a real problem glad I don't live in USA.
Speaking as somebody who grew up in Britain and spent years working with "straight" 240V, I really don't see as much of a problem here in the U.S. with 120V as seems to be commonly believed back in the U.K. Obviously voltage-drop concerns (and safe current-carrying capacity) necessitate larger conductors for a given load, but it's just a matter of scale. The biggest problem seems to be with things like people trying to run power tools with heavy start-up surges on very long, undersized extension cords. Plug your Skilsaw into a 100 ft. 18-gauge extension cord and you're bound to have trouble, just as can happen with people trying to use long 0.75 sq. mm extension leads for heavy loads in Britain or Ireland.
Remember that the heaviest loads in homes generally run on 240V anyway - The electric range, clothes dryer, large fixed heating and air conditioning units, etc. Admittedly the standard 120V general-use outlets do limit the power of portable heaters and similar appliances, but that's probably the most restrictive aspect of the system.
In UK neutral is considered as live so we call phase wire line I think you call it the hot wire?
There was a time when the neutral was
not considered to be a live conductor though. I think it changed with the 15th edition, or possibly a later revision.
"Hot" is something of a colloquialism. The NEC terminology refers to it as an
ungrounded conductor, as opposed to a
grounded conductor (which may or may not be a neutral in the true sense, which the NEC retained long after the IEE defined it as any earthed circuit conductor, regardless of whether it was carrying only imbalance current or not). Perhaps somewhat confusingly upon first reading, the NEC then uses the term
grounding conductor to refer to a protective earth/ground wire.
sounds right !I left Dublin in1981 worked with a English bloke back then he was an electrician working in dub at the time. He knew his stuff
Were main ELCB's (voltage or current types) ever used extensively in Ireland in the past? I know that these days ESB requires all new services to be wired as TN-C-S ("neutralizing" the earth system of the installation as they put it), but I don't know how far back that rule goes.
I remember when ELCB's came out in Ireland. Not sure if current or voltage but I would say voltage
It had to of been close to fourthy years ago . I was serving my time with an electrical contractor wiring houses out in Bray, Co Dublin
The ESB did neutralizing of the earth system back then to the best recollection
There seems to be something wrong with the math here? I would start getting concerned with VD with 15amps load on 120 v over 200' our coils of #14 comes in 250' roll
Remember K is 10.4 ohms per mil foot of copper not 2.57ohms per 1000'
based on ED= kIL/CSA
Not sure how you came up 46'
Yes, the specific resistance of copper is a little over 10 ohms per cmil-ft., but that does equate to 2.57 ohms/M ft. for #14 at 25 deg. C. (as per NEC tables).
120V x 3% = 3.6V
3.6V / 15A = 0.24 ohm maximum permissible resistance
0.24 / 2.57 x 1000 = 93 ft. approx.
But that's for
both conductors. So half of that for the maximum cable length.
Correction ..according to my math 120volt #14 wire would be good with a 15amp load 80' keeping within 3%
At 80 ft. you'd have over 5% voltage drop.