Fault finding can take a long time, however in this case - what faults? Test results do not indicate any faults.what we're saying is that it's a right old rigmarole to do any fault-finding
Fault finding can take a long time, however in this case - what faults? Test results do not indicate any faults.what we're saying is that it's a right old rigmarole to do any fault-finding
To be fair, we don't know that for sure - it could just be stupid recording on the form of something which really is a fault - i.e,. "<1,000" might actually mean 0.5 MΩ.Fault finding can take a long time, however in this case - what faults? Test results do not indicate any faults.
Quite so.There appears to be a HUGE disconnect here, but it might be my layman understanding. My Electrician appears to have marked some circuits with C2 because they measured at something less than 1,000MΩ... we don't know what yet... obviously there's a range of 0MΩ up to 999MΩ I guess. .... But the comment from JohnW2 says they could be OK as "low as 1 MΩ without necessarily attracting any code, let alone a C2"... if they were, for example, 150MΩ and 666MΩ I guess we could say the C2s are marked incorrectly on this EICR?
Again, quite so - that's a question that only he could answer.If that is the case it makes me wonder why he marked <1,000MΩ... as though it was some kind of boundary measurement that was important to the C2 rating. Why not <1MΩ?
Insulation resistance tests the quality of the insulation on the cables/wires, and will often detect other problems such as moisture, dirt or grease at terminals of sockets, switches and other items.There appears to be a HUGE disconnect here, but it might be my layman understanding.
I really think it's very premature to even consider that question. The IR measurements and associated comments currently make no real sense, such that there may well be no problem at all, let alone a need for a 're-wire'.There seems to no way to answer the question as to if it needs a rewire.
Yes, think of it like a two-digit thermometer in Fahrenheit.Fair comment. I think (without verification from him yet) that it potentially betrays the Electrician thinking something is special about 1000MΩ though... marking results as <1000MΩ and C2 and saying there is a insulation resistance issue that leads to the need for a re-wire... might be all OK (and inarguable)... but the documentation simply doesn't back that up, yes? There should be a number there... a number expected to be <1MΩ?
Please do bear with me if I'm repeating myself. It's hard to discuss something with an authority / expert when you have none yourself.