Murdochcat said:
As it’s over 20 years since RCD protection entered the regs, I think a C2 in this case is justified.
NOTHING to do with how long ago it was/was not allowed. That is irrelevant. It is effectively how actually serious is the issue?
I totally agree today all should be RCD protected, but as to C3 or C2 that is another question. May be better with another thread, I remember going into the control room of a lifting bridge and there were still open knife switches, which were allowed when the bridge was built, but are extremely dangerous. Today it would be a code C1, so there is a case for saying even if allowed when built and nothing has changed lack of RCD should not be permitted.
However September last year solar panels fitted to my house, with an UPS included, and as a result the central heating is no longer RCD protected and I have a compliance certificate for that job. Not plug and socket, it's a FCU but still today circuits without RCD protection it seems comply. This summer I will look to change this.
Seem to remember BS 7671:2001 required RCD protection for sockets likely to be used outside, but it was not until BS 7671:2008 that all sockets needed RCD protection so not quite 20 years.
However if one does work, and on omits to inform the person in charge of the building of any danger, could simply be an oil spill. Then if there is an accident one could be taken to court by the HSE. Any health and safety issue must be in writing, phone call is not enough, it could be email, SMS, or note, but has to be in writing. However not seen any time scale as to how fast it must be done. But would expect the courts would consider it should be same day.
Personally if I found C1 or C2 items I would want to inform before I had got around to writing out the full report.