Of course they could. They decide that it is not in the public interest to pursue enforcement.If they were playing by the rules, they would/could not really just say "Goodbye"
Of course they could. They decide that it is not in the public interest to pursue enforcement.If they were playing by the rules, they would/could not really just say "Goodbye"
Hence, although any electrical work should result in an EIC or MWC
Well, yes, they could 'give up', but that's probably no problem for whoever had the work done. If a potential buyer in the future asks for a Completion Certificate, they can simply be referred to LABC to explain why they did not find a way of facilitating issue of a Certificate. In practice, I strongly suspect that they would not want the untidiness of refusing to issue a Certificate (but not doing anything further about the situation), so would probably usually find a way of issuing a Certificate.Of course they could. They decide that it is not in the public interest to pursue enforcement.If they were playing by the rules, they would/could not really just say "Goodbye"
The dreaded "like for like" again (which I've personally never seen in any regulation) - where does that (and, indeed, all of what you're saying) come from? Would you really say that 'like for like' replacement of, say, all of the sockets and cable in a circuit did not require any certificate?Like-for-like replacement is classified as maintenance work, and does not require a MEIWC to be issued.Hence, although any electrical work should result in an EIC or MWC
Whilst I agree with John regarding the 'like for like' - where appropriate the regulations merely state 'replacement' so clearly allow not 'like for like' replacements.Like-for-like replacement is classified as maintenance work, and does not require a MEIWC to be issued.Hence, although any electrical work should result in an EIC or MWC
Quite so. In any event, if it ever did say "like for like", one would have to try to define what that meant, since replacements parts after a period of time are very often not going to be absolutely identical to the originals.Whilst I agree with John regarding the 'like for like' - where appropriate the regulations merely state 'replacement' so clearly allow not 'like for like' replacements.
Again, quite so, and that was the issue Risteard was addressing. I would say, like you, that any work which required any testing (and some would undoubtedly argue that that means any work) ought to result in an IEC or MEIWC, if not only as a means of documenting the results of that testing.As for not requiring a MEIWC, this may be acceptable for a light switch, for example, but I would be most uneasy when replacing a shower. So, if, as I would, testing the circuit then you may as well give the customer a copy of the results.
That may be true in the ROI (I wouldn't know).Like-for-like replacement is classified as maintenance work, and does not require a MEIWC to be issued.
Indeed so. In fact, in terms of your example, not only does replacing a CU require an EIC but "replacing a CU" (although not, in England, installing a new one ) is notifiable work!That may be true in the ROI (I wouldn't know). But it is not true here. Replacing items can easily require an MEIWC to be issued, or even an EIC (replacing a CU for example, even if the underlying reason is maintenance and the new one is identical to the old).Like-for-like replacement is classified as maintenance work, and does not require a MEIWC to be issued.
I live in the north of Ireland, although I work on both sides of the border.That may be true in the ROI (I wouldn't know).Like-for-like replacement is classified as maintenance work, and does not require a MEIWC to be issued.
But it is not true here. Replacing items can easily require an MEIWC to be issued, or even an EIC (replacing a CU for example, even if the underlying reason is maintenance and the new one is identical to the old).
Where is the scope of this 'maintenance work' defined? As BAS asked by implication, would it include, for example, replacing a mechanically damaged CU with an identical one?However, I can assure you that there is no BS 7671 requirement to issue a Minor Electrical Installation Works Certificate for maintenance work such as like-for-like replacement of accesories, although it may be prudent to do so.
I didn't read the words - just looked at the flag image.I live in the north of Ireland,
Does it define "maintenance"?However, I can assure you that there is no BS 7671 requirement to issue a Minor Electrical Installation Works Certificate for maintenance work such as like-for-like replacement of accesories, although it may be prudent to do so. (Indeed the guidance for recipients section states that it may be used for the replacement of accessories.)
Fair enough. That obviously makes sense, and is 'expected', but I need to reach for my books to investigate this "etc."!EDIT in response to JohnW's post above. ... The text in GN3 and the regs specifically states that an MWEIC does not apply to the replacement of consumer units etc.
To this reader, that reading is so bl****ng obvious that it has never, ever occurred to me that anybody could possibly "read" it any other way."For an addition or alteration which does not extend to the introduction of new circuits, a MEIWC may be used."
I read that 'may' as 'may be used instead of EIC'; not 'may or may not bother with any certificate'.