Recentky looking at the ratings of Wago connectors, I was reminded how different the EN and UL current ratings of items can be. For example, with 221-61x Wagos (for conductors up to 6mm²), the EN rating (which is the one we would look at) is 41 A, whereas the UL one is only 30 A.

I wonder whether the UL figures are 'over-cautious', the EN ones 'not cautious enough', or what?
 
Sponsored Links
A few things I observe.

1. The EN ratings seem to be "odd" numbers, while the UL ratings are standard american circuit ratings.
2. The americans seem to be a bit more cautious on default wire sizes for a given current than we do.
3. The largest american conductor size the connectors support is 10AWG which is a fair bit smaller than 6mm²

IIRC the next american breaker size over 30A is 40A, which would normally require 8AWG wire, which is too big for the wago.
 
A few things I observe.

1. The EN ratings seem to be "odd" numbers, while the UL ratings are standard american circuit ratings.
2. The americans seem to be a bit more cautious on default wire sizes for a given current than we do.
3. The largest american conductor size the connectors support is 10AWG which is a fair bit smaller than 6mm²

IIRC the next american breaker size over 30A is 40A, which would normally require 8AWG wire, which is too big for the wago.
As for your (1), I suspect the 41 A may relate to the fact that 6mm might be on a 40A OPD?
I agree about the rest.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top