Extending Cooker Feed - Notifiable?

Outside socket - yes it is.
Excellent. And presumably if instead some swa was hard wired onto the end of it inplace of the socket and ran that to the garage, thus putting the socket inside, that would still be notifiable?
Yes
Why do you say that? Are you 'quibbling' about the fact that the connection between existing cable and extension would (presumably) be in a kitchen? Apart from that, I can't see why extending an existing circuit to provide a socket (which is not part of an 'outside electrical installation') would be notifiable.

Kind Regards, John
 
Sponsored Links
Yep, you could also argue the SWA run outside is a special installation. Now there is talk of a garage CU also.
 
Yep, you could also argue the SWA run outside is a special installation.
We've been through that before, and I thought the general consensus was that, although it's surprising that running an outdoor, maybe underground, cable should be non-notifiable, the wording of Schedule 4 certainly seems to indicate that it is not, per se, provided that it is terminated 'indoors' (house or outbuilding) at both ends.
Now there is talk of a garage CU also.
Indeed, and that would obviously move the goalposts. However, I was responding to a question about running SWA from the circuit in a kitchen to a socket in an outhouse.

Kind Regards, John
 
Sponsored Links
running SWA from the circuit in a kitchen to a socket in an outhouse.
Not notifiable.
Quite - as I said/implied ... provided, of course, that one does not quibble (and I know/presume that you won't!!) about the fact that one would (presumably) be installing an accessory (JB or whatever) within a kitchen to effect the join.

Kind Regards, John
 
Quibble away, and then deal with the fact that your quibbling means that there is no longer any non-notifiable work where a junction box is used as there is no mention of them in Schedule 4.
 
Quibble away, and then deal with the fact that your quibbling means that there is no longer any non-notifiable work where a junction box is used as there is no mention of them in Schedule 4.
It's not the existance of JB which is the issue - and I disagree with what you say, since neither is there any mention of cable in relation to (non-notifiable) extensions to add sockets, FCUs, lights and switches. I will therefore happily interpret the Schedule as meaning that things like cable and JBs are implicitly allowed as part of these works that can be done without notification.

The issue is about the location of the JB in a kitchen - but, as you know, I'm not really one to quibble about this. True, I am not completely sure of the intention of Schedule 4 as regards this - but, as I've said, even if the intention of the law is to require such a thing to be notified, then that is a law which I would happily and comfortably break.

Kind Regards, John
 
It's not the existance of JB which is the issue - and I disagree with what you say, since neither is there any mention of cable in relation to (non-notifiable) extensions to add sockets, FCUs, lights and switches.
Why does that mean that you have to disagree?

Surely if there is no explicit mention of them then they are implicitly included in the notifiable/non-notifiable status of the item being added.


I will therefore happily interpret the Schedule as meaning that things like cable and JBs are implicitly allowed as part of these works that can be done without notification.
Indeed. So we are agreed, then.


The issue is about the location of the JB in a kitchen
For the purposes of Schedule 4 its location has to be that of the item of which it is an implicit part. If it inherits that part's notifiability status it inherits its location.


but, as you know, I'm not really one to quibble about this. True, I am not completely sure of the intention of Schedule 4 as regards this - but, as I've said, even if the intention of the law is to require such a thing to be notified, then that is a law which I would happily and comfortably break.
You don't have to break it.

You just have to think logically, and you'll see that you would not be breaking it.
 
The issue is about the location of the JB in a kitchen
For the purposes of Schedule 4 its location has to be that of the item of which it is an implicit part. If it inherits that part's notifiability status it inherits its location.
We know your view/interpretation - and you may be right - in which case, as you say, I wouldn't need to break the law. However, if you're wrong I would, in this case, break the law.

Kind Regards, John
 
No discrimination.
Ive done some reading on discrimination.

What would you usually do to add some of that then? Short of up'ing the cable or seriously derating the final circuits I dont see how you would? Can you get a slow-blow fuse to protect the cable.

Obviously I can see that the lights going off becuase of a fault/overload on the power circuit is not ideal, although as far as I know at my parents the garage comes off a 30amp mcb with 6mm, and then had a 32amp ring main and 6amp lighting.


Daniel
 
Ive done some reading on discrimination. What would you usually do to add some of that then? Short of up'ing the cable or seriously derating the final circuits I dont see how you would? Can you get a slow-blow fuse to protect the cable.
In your case, the simplest solution is not to 'add in discrimination' but, rather to reduce the number of overcurrent protective devices (OPDs - MCB/fuse) to one - so there are not two things to 'discriminate' between. An OPD is only there to protect the cable. Provided all cable is fat enough to be adequately protected by the OPD at the house CU, there is no need for any MCB/fuse anywhere else. If you want to run a 'sub-circuit' in smaller cable (e.g. for lighting), then you can take that off the main supply via a fused connection unit (FCU), with a fuse in that small enough to protect the size of cable concerned (say 3A or 5A). That should discriminate satisfactorily with, say, a 20A or 32A MCB in the CU.

Kind Regards, John
 
In your case, the simplest solution is not to 'add in discrimination' but, rather to reduce the number of overcurrent protective devices (OPDs - MCB/fuse) to one - so there are not two things to 'discriminate' between.
I see, so I would just have the MCB in the consumer unit, which would protect the cable and everything beyond it, with then a 5amp FCU to the lighting.

Interesting.

Although obviously, should I overload the power circuit, I would still loose all lighting. Unless there was some emergancy lighting.


Daniel
 
I see, so I would just have the MCB in the consumer unit, which would protect the cable and everything beyond it, with then a 5amp FCU to the lighting. Interesting.
Exactly. That's the usual 'simple' supply to a garage.
Although obviously, should I overload the power circuit, I would still loose all lighting. Unless there was some emergancy lighting.
Sure, but that's unavoidable unless you either run a totally separate circuit from house to garage for the lighting (with its own MCB in house), or run a fat cable (hence allowing a high rated MCB at CU) all the way from house CU to a CU in the garage (which could then give you discrimination between MCB in house and power circuit MCB in garage). As regards the latter, the 4mm² cable in your existing cooker circuit would limit you to a 32A MCB, which is not hih enough to give you discrimination from a 20A (and probably not 16A) power circuit MCB in the garage. If you could run 6mm² or 10mm² cable all the way from house CU to a garage CU, things would be different, because you could then have a higher-rated MCB in house.

Kind Regards, John
 
Just how high would you need to go to attain discrimination upstream from a B32?

My garage/workshop has a 32A ring and a 6A lighting circuit and is fed from a 40A MCB on the main CU, over i believe 10mm SWA. The spark that fitted it was a lazy * and actually made out it was a GOOD thing that there were now two RCD's on the garage supply (one on the main CU and one in the garage CU).

Ofcourse i now realise this is rubbish (having tripped out the garage at one point and taken out the house with it) and its apparent the discrimination issues mentioned here with the B32 and B40 are also crap.
 
Just how high would you need to go to attain discrimination upstream from a B32?
In the face of high fault currents, I don't think one could ever guarantee discrimination, no matter what the ratio of MCB ratings. However, to stand a reasonable chance of getting discrimination, you would need at least a 2:1, probably 3:1 ratio - e.g. you might get discrimination between, say, a B6 and a B16. In other words, I don't think you would, in practice, find an MCB to put upstream of a B32 which would offer much hope of discrimination (and, even if you could, you'd have to use hefty cable). If the upstream device is a fuse, then you're much more likley to get discrimination but, even then, I think you'd still need at least 2:1.
My garage/workshop has a 32A ring and a 6A lighting circuit and is fed from a 40A MCB on the main CU, over i believe 10mm SWA. The spark that fitted it was a lazy * and actually made out it was a GOOD thing that there were now two RCD's on the garage supply (one on the main CU and one in the garage CU). Ofcourse i now realise this is rubbish (having tripped out the garage at one point and taken out the house with it) and its apparent the discrimination issues mentioned here with the B32 and B40 are also crap.
Indeed. Of course, in the case of two 30mA RCDs, there's no reason to even expect any discrimination. The only 'upside' of have two RCDs is that their reliability is uncertain (one often hears it quoted that about 7% are found to be faulty when tested), so there's some 'belt and braces' reassurance to be derived by having two!

Kind Reards, John
 