Extending Cooker Feed - Notifiable?

If you could run 6mm² or 10mm² cable all the way from house CU to a garage CU, things would be different, because you could then have a higher-rated MCB in house.
Yes, ok.

And ofcause that would require re-running a cable through the house, and spending twice as much on the swa running down the garden. Circuit lenght is around 12m inside and 8-10 outside.

Daniel
 
Sponsored Links
In the face of high fault currents, I don't think one could ever guarantee discrimination, no matter what the ratio of MCB ratings. However, to stand a reasonable chance of getting discrimination, you would need at least a 2:1, probably 3:1 ratio - e.g. you might get discrimination between, say, a B6 and a B16. In other words, I don't think you would, in practice, find an MCB to put upstream of a B32 which would offer much hope of discrimination (and, even if you could, you'd have to use hefty cable). If the upstream device is a fuse, then you're much more likley to get discrimination but, even then, I think you'd still need at least 2:1.
So if you where doing a 'perfect job' you would have a 60amp fuse at the CU, leading to 10mm csa cable, then the garage CU with you 32amp final circuit MCB/RCBO.

Daniel
 
So if you where doing a 'perfect job' you would have a 60amp fuse at the CU, leading to 10mm csa cable, then the garage CU with you 32amp final circuit MCB/RCBO.
Yep, I suppose that's about it - but for the average person who wants just a socket or three and some lighting in a garage, to do that just to achieve discrimination could well be regarded as rather 'OTT'!

Kind Regards, John
 
Yes, well at the moment, and for the last 14months ive had an extension out of the conservatory window, over the paving, under the garage wall and terminating in a 6way cabled tied to the framework from which everything in run, which it not overly diverse!

But it sounds as I could have some 4mm SWA run from the 4mm cooker feed by the external wall, along the fence and into the garage, junction box to terminate, and then a ring main or radial of sockets, off which came a 5amp FCU to the lighting ring. If i wanted a 16amp socket in future for a larger welder take that of the ring main with another fcu.


Daniel
 
Sponsored Links
didnt think you could put a ring on the end of a piece of cable like that anyway?
I dont know, im just speculating what could be done. What you would do if you didnt do that then, predumably just a radial in 4mm daisy chaining socket to socket? I guess you could have two radials from the JB (which would be on the back wall) one down each side? Just seems logial to make it into a ring but if thats not ok, clearly not.



A 16 amp socket should really be on a dedicated radial.
From what though? The junction box rather than the ring main, its not going to be dedicated right back to the house is it.


My current welder is a 150amp esab inveter mig which welds well off a 13amp socket, so its not a deal breaker, more of a 'if ive got an spark, he might as well future proof'.


Daniel
 
didnt think you could put a ring on the end of a piece of cable like that anyway?
I can't see any electrical reason why not, provided that the cable up to the ring is of large enough CSA and (as discussed) protected by a 32A MCB - after all, that's no different from having a sub-main to a distant CU, from which a ring then originates. What one obviously can't do is, say, have a 2.5mm² ring connected back to the CU (and 32A MCB) via a single 2.5mm² cable. Having said that, I really don't see why Daniel needs a ring.

Kind Regards, John
 
Ive done some reading on discrimination.
You should now do some reading on what the Wiring Regulations say about avoiding hazards and minimising inconvenience in the event of a fault, taking account of danger that may arise from the failure of a single circuit such as a lighting circuit, taking account of the consequences of the operation of any single protective device, and so on.


Obviously I can see that the lights going off becuase of a fault/overload on the power circuit is not ideal,
It could be a lot more serious than "not ideal".


although as far as I know at my parents the garage comes off a 30amp mcb with 6mm, and then had a 32amp ring main and 6amp lighting.
Lazy, bad design, and arguably in contravention of the Wiring Regulations. The fact that it is commonly done changes none of those.
 
If you could run 6mm² or 10mm² cable all the way from house CU to a garage CU, things would be different, because you could then have a higher-rated MCB in house.
Or, even better, a switchfuse in the house - get it off the CU altogether.
 
If you could run 6mm² or 10mm² cable all the way from house CU to a garage CU, things would be different, because you could then have a higher-rated MCB in house.
Or, even better, a switchfuse in the house - get it off the CU altogether.
Indeed so. However, as I said, whether such is justified for the average garage supply is another matter. As has been implied in this thread, if we advised people that such an 'even better'/ideal approach was the way it 'must' be done, then many would probably resort to an extension lead chucked out of some window, which is probably the least ideal 'solution'!

Kind Regards, John
 
I being the person responsible for the design of the electrical installation (as indicated by my signature below), particulars of which are described above, having exercised reasonable skill and care when carrying out the design hereby CERTIFY that the said work for which I have been responsible is to the best of my knowledge and belief in accordance with BS 7671:2008 including the requirements for avoiding avoiding hazards and minimising inconvenience in the event of a fault, for taking account of danger that may arise from the failure of a single circuit such as a lighting circuit, for taking account of the consequences of the operation of any single protective device, and so on, none of which are, to the best of my knowledge and belief, qualified in BS 7671:2008 as not applying to an average garage.

As I said - the fact that it's often done badly does not mean that it's not actually done badly.
 
I being the person responsible for the design of the electrical installation ... none of which are, to the best of my knowledge and belief, qualified in BS 7671:2008 as not applying to an average garage.
Utopia is a fairly attractive concept, but probably much more boring, and maybe less fun, than the real world.

Kind Regards, John
 
Ah well - one man's boring and less fun electrical design is another's professionalism and sense of responsibility and duty of care, I guess.
 
Ah well - one man's boring and less fun electrical design is another's professionalism and sense of responsibility and duty of care, I guess.
Maybe. Professionalism does not necessarily preclude (indeed, probably should include) realism, common sense and case-by-case risk assessments - and, in the case we're discussing, there is enough wiggle room in the wording of the regs to allow professionals to make some decisions on their own, rather than having to act as robotic followers of a cookbook - i.e. be proper professionals.

Kind Regards, John
 