The charger itself is also only rated at 10AAlso interesting to me... Is the plug only rated at 10A?
View attachment 252120
The charger itself is also only rated at 10AAlso interesting to me... Is the plug only rated at 10A?
View attachment 252120
According to ISO:This View attachment 252126 is the bit that interests me. Does that mean it auto disconnects the earth with fault conditions?
There is always the possibility of faults.Regarding the RCD, even if i install the above, is there still a possibility of DC faults then
My sons mate has a Tesla and they charged that from a plug socket when they went to Wales. Took about 13 hours or so.I didn't know you could charge a PHEV with a 13A plug.
That makes life much easier if you drive to visit someone who does not have a charging point.
Our outside socket, used for pressure washer/vacuum cleaner/Christmas lights is just connected to our downstairs ring main via a switched spur inside the house.I don't want the expense or need the speed of a proper wall-charger like an Ohme or a Zappi as we are likely moving house next year so the 3 pin outside double socket will suffice
There is always the possibility of faults.
Devices which can create DC faults can't be installed downstream of a type AC RCD, as those DC faults won't be detected and can stop the RCD from working for AC faults.
The most obvious solution is to have a new circuit for the outdoor socket from a Type A RCBO, installed into the spare #4 way in the consumer unit.
20A isolator switch inside if desired, and a single unswitched socket outlet outside.
There is always the possibility of faults.
Devices which can create DC faults can't be installed downstream of a type AC RCD, as those DC faults won't be detected and can stop the RCD from working for AC faults.
The most obvious solution is to have a new circuit for the outdoor socket from a Type A RCBO, installed into the spare #4 way in the consumer unit.
20A isolator switch inside if desired, and a single unswitched socket outlet outside.
There is always the possibility of faults.
Devices which can create DC faults can't be installed downstream of a type AC RCD, as those DC faults won't be detected and can stop the RCD from working for AC faults.
The most obvious solution is to have a new circuit for the outdoor socket from a Type A RCBO, installed into the spare #4 way in the consumer unit.
20A isolator switch inside if desired, and a single unswitched socket outlet outside.