Fitting consumer unit vertically

All it states is: ......... As above, I cannot find the technical documentation.
Fair enough. That Annex ZB test is, of course, a conditional test, which requires the device to withstand a 16kA test current when there is a 100A upstream fuse (even though it could not necessarily safely break 16kA in the absence of that fuse).

Kind Regards, John
 