First I must appologise because I replied having read a very basic question and jumping to the conclusion that it could not be an RGI.
I also inadvertently said some might have to be in 32 mm when that is not a standard UK copper tube size.
So to try to answer the probable original question with a more general answer!
You work out all the equivalent lengths after taking elbows and "T" outlets to 90 degree branches ( !!! ) into account.
You then assume for the calculation that all appliances are on and taking their maximum rated power input.
You do the calculation for each section and note the pressure drop for each section. The last section of "about 20 m" comes after the first section and say the drop in the first section is 0.4 mB then the last section can only drop 0.6 mB.
Thats my understanding of the way the calculation is aproached and using those figures then part of the pipe would have to be greater than 28 mm.
Tony
I also inadvertently said some might have to be in 32 mm when that is not a standard UK copper tube size.
So to try to answer the probable original question with a more general answer!
You work out all the equivalent lengths after taking elbows and "T" outlets to 90 degree branches ( !!! ) into account.
You then assume for the calculation that all appliances are on and taking their maximum rated power input.
You do the calculation for each section and note the pressure drop for each section. The last section of "about 20 m" comes after the first section and say the drop in the first section is 0.4 mB then the last section can only drop 0.6 mB.
Thats my understanding of the way the calculation is aproached and using those figures then part of the pipe would have to be greater than 28 mm.
Tony