Many thanks twgas and D.Hailsham.
I have just followed D.Hailsham's test guide and was confounded by the results to the very first test which shows 57v on cylinder stat T1 (black wire). This is with the stat turned down, which if I understand it correctly means that TC is connected to T2 and T1 should be left floating.
I measured the voltages on the terminals in the cylinder stat during the first test, because I did not believe what I was seeing, and T1 was indeed 57v which must be wrong, but is this enough to cause a problem. I noted that TC and T2 in the cylinder stat (which should be connected together) were both showing 240v, presumably from HWOFF on T2.
I have attached the results of D Hailshams test here,
http://www.mhr.me.uk/docs/voltagechecks20052011.doc
So it seems there is a false signal of 60 - 100 v at different times on T1, when there shouldnt be. The question is how many volts are required for a boiler to think it is being switched on. In actual fact, the real problem happens when the boiler is already running, and fails to turn off when CH is satisfied. So perhaps the question should be, how few volts are required for the boiler to think it is being turned off.
Does this evidence suggest it is worth changing the cylinder stat ?
Your thoughts please
I really appreciate your time.
I have just followed D.Hailsham's test guide and was confounded by the results to the very first test which shows 57v on cylinder stat T1 (black wire). This is with the stat turned down, which if I understand it correctly means that TC is connected to T2 and T1 should be left floating.
I measured the voltages on the terminals in the cylinder stat during the first test, because I did not believe what I was seeing, and T1 was indeed 57v which must be wrong, but is this enough to cause a problem. I noted that TC and T2 in the cylinder stat (which should be connected together) were both showing 240v, presumably from HWOFF on T2.
I have attached the results of D Hailshams test here,
http://www.mhr.me.uk/docs/voltagechecks20052011.doc
So it seems there is a false signal of 60 - 100 v at different times on T1, when there shouldnt be. The question is how many volts are required for a boiler to think it is being switched on. In actual fact, the real problem happens when the boiler is already running, and fails to turn off when CH is satisfied. So perhaps the question should be, how few volts are required for the boiler to think it is being turned off.
Does this evidence suggest it is worth changing the cylinder stat ?
Your thoughts please
I really appreciate your time.