Both inside the installation, and outside the installation, and to what order of magnitude?
I'm just curious.
Discuss.
I'm just curious.
Discuss.
I'm not sure what you're thinking of here. Loads will surely only affect PSCC if they result in a change of voltage as seen at the installation, since the only other factor is the measured L-N loop impedance, which I wouldn't expect to be influenced (significantly, if at all) by loading. What are you thinking of?Both inside the installation, and outside the installation, and to what order of magnitude? I'm just curious. Discuss.
That's exactly what I was thinking ofthe only other factor is the measured L-N loop impedance, which I wouldn't expect to be influenced (significantly, if at all) by loading. What are you thinking of?
I would say the latterThat's exactly what I was thinking of ... You are part of an LV network fed by a single MV:LV transformer. If you have a combined resistive load of other consumers of 144A, that represents an impedance on the network of 1.6Ω. If the feed transformer also has an impedance of 1.6Ω, simplistically this means you will see 0.8Ω at your service head. ... This would be a false reading, and double your recorded PSCC vs reality. If you are on TN-C-S, I would have thought this also affects your Ze. ... No? Yes? Or have I missed something fundamental?
If the load had an impedance of 1.6 ohm and the source also had an impedance of 1.6 ohm then the loaded voltage would be half the open circuit voltage. I don't think anyone would consider that acceptable.You are part of an LV network fed by a single MV:LV transformer. If you have a combined resistive load of other consumers of 144A, that represents an impedance on the network of 1.6Ω. If the feed transformer also has an impedance of 1.6Ω
That's obviously true, but it doesn't alter what I said about the measurements.If the load had an impedance of 1.6 ohm and the source also had an impedance of 1.6 ohm then the loaded voltage would be half the open circuit voltage. I don't think anyone would consider that acceptable. ... To keep voltage reasonablly stable the source impedance needs to be much lower than the likely load impedance.You are part of an LV network fed by a single MV:LV transformer. If you have a combined resistive load of other consumers of 144A, that represents an impedance on the network of 1.6Ω. If the feed transformer also has an impedance of 1.6Ω
Wrong.With mfarrow's (hypothetical and, as you say, impractical) scenario, a conventional live L-N loop impedance measurement, using the supply tranny as the source, would still give the correct answer of 1.6Ω for the supply/source impedance, since none of the test current being observed would flow through the load.
Yes, you're right. I let myself get confused my mfarrow's talk about resistances. The point in my mind, in response to what he actually asked about in his OP, was the one you've just made (that the PSCC would be measured correctly, deven in the face of massive loads on the network) - but, as you say, a ('pre-test') reduction in supply voltage (at installation) due to such massive loads on the network would result in an incorrect calculation of supply impedance.Wrong. ... Now suppose we add a 1.6 ohm load and use our tester again. This time the tester measures an "open circuit"* voltage of 120V and a short circuit current of 150A and calculates an impedance of 0.8 ohm. ... The PFC on the other hand wont change between the two tests, in either case it remains at 150A.With mfarrow's (hypothetical and, as you say, impractical) scenario, a conventional live L-N loop impedance measurement, using the supply tranny as the source, would still give the correct answer of 1.6Ω for the supply/source impedance, since none of the test current being observed would flow through the load.
Needless to say, they don't use (negligible impedance) short circuits! They introduce a non-negligible-impedance 'fault' for a very short period of time and measure the consequential brief drop in measured voltage. At 230V, my Fluke uses a maximum of 12A for 10msec - i.e. it introduces a 'fault' (L-N or L-E) of about 19Ω for 10msec.I'm still unconvinced how the meter actually works though? How does it do a controlled short circuit? Surely everyone's lights must dim?
All this talk about VDs in supply cables has got me thinking (always dangerous!) ... something doesn't seem to add up.If the load had an impedance of 1.6 ohm and the source also had an impedance of 1.6 ohm then the loaded voltage would be half the open circuit voltage. I don't think anyone would consider that acceptable. To keep voltage reasonablly stable the source impedance needs to be much lower than the likely load impedance.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local