Whilst your figures are obviously correct, I think you may be over concerned by numbers and W2 Towers.
Although adjustments will undoubtedly have to be made in very large houses, commercial and industrial installations, here in 'normal' domestic property land where a circuit's maximum Zs rarely gets above half the maximum figure of the BGB values, therefore there is nothing to worry about or calculate, I don't think it will make any difference.
Even in the case of 50A and a maximum Zs now of 0.7Ω where Ze is half of this the reduction is only 10% and still allows a 10mm² cable of over 50m.
The last shower I installed had a Zs of 0.27Ω.
I am still wondering why this has been brought up now or why it hasn't been before.
It may be sensible to allow for the minimum voltage in this example and the maximum voltage in others but it does negate the need or application ever of a nominal voltage.
I realise it may be optimistic to expect all electricians, especially these days, to be able to do all the calculations themselves but unless they can there may have to be a very large OSG in the future.
I am minded of the previous (15th) requirements for bonding everything regardless and then the presumed enlightenment of subsequent regulation writers.
After all the physics hasn't changed much in the last one hundred and fifty years, has it?
So, why do the regulations?
Although adjustments will undoubtedly have to be made in very large houses, commercial and industrial installations, here in 'normal' domestic property land where a circuit's maximum Zs rarely gets above half the maximum figure of the BGB values, therefore there is nothing to worry about or calculate, I don't think it will make any difference.
Even in the case of 50A and a maximum Zs now of 0.7Ω where Ze is half of this the reduction is only 10% and still allows a 10mm² cable of over 50m.
The last shower I installed had a Zs of 0.27Ω.
I am still wondering why this has been brought up now or why it hasn't been before.
It may be sensible to allow for the minimum voltage in this example and the maximum voltage in others but it does negate the need or application ever of a nominal voltage.
I realise it may be optimistic to expect all electricians, especially these days, to be able to do all the calculations themselves but unless they can there may have to be a very large OSG in the future.
I am minded of the previous (15th) requirements for bonding everything regardless and then the presumed enlightenment of subsequent regulation writers.
After all the physics hasn't changed much in the last one hundred and fifty years, has it?
So, why do the regulations?