No, it is for anything up to the current carrying capacity of the cable.This surprised me somewhat as I thought 1.5mm was for lighting circuits.
1mm² T&E is used for 6 Amp lighting circuits and that is hugely oversized.
No, it is for anything up to the current carrying capacity of the cable.This surprised me somewhat as I thought 1.5mm was for lighting circuits.
There’s a CEF branch 5 mins drive away and they sell this by the metre which is very handy.Yeah.you wrap the cable around the screw in a clockwise direction.
Half way round the screw is plenty.
I’m sure you will do it fine.
The raised bit of metal traps it in place.
Ideally use this cable.
3 Core HO7RNF Rubber Flexible Cable
1.5mm
I think b and q sell it
Fair enough - and, as you point out, that will be not be materially different to what you had before (which I imagine probably all worked satisfactorily for a long time).So my final setup is….. I have 2 of these AEG single ovens with each rated at 2.79 kW. ... For each oven, I’ll use 1m length of that recommended 3 core cable and then I’ll connect a 13A MK toughplug to the other end. .... Each oven will be plugged into separate double sockets, both of which are part of the kitchen ring main. The spare socket on one of them will be used to power a full height integrated fridge, and the other a full height integrated freezer. .... These new ovens are direct replacements for 2 hotpoint ovens rated at 2.6 kWwhich came supplied with a cable and 13A plug.
No, as far as currents (hence potential 'overloading') is concerned, that would be no different from using plugs.Would it make any material difference if, instead of putting a 13A plug on them and plugging them into a standard socket, I connected them to a 13A FCU which was in itself, also on the kitchen ring main ?
Fair enough.Other things of note on that circuit would be kettle, toaster, microwave and air fryer but the likelihood of all these going at same time as 2 ovens is very slim. TBH, even running 2 ovens at same time only happens 2 or 3 times a year round xmas/new year. ... Dishwasher is there as well but we tend to run that overnight on a cheaper tariff. Washing machine and tumble dryer are on a different circuit in utility room.
Indeed - and, as I said, in practice it's most unlikely to ever happen. A 32A MCB should take about an hour to trip with about 46A flowing, and longer for lower (but greater than 32A) currents - and it's very unlikley that would ever happen. Such an MCB should never trip with currents less than about 36A.In the event I did have loads running and I exceeded the 32A limit of the breaker on the board, would it just be a case that the breaker would trip with no damage to cables/appliances ?
Hi again…Evri have played a blinder and lost my MK Toughplug package. Are there are any other heavy duty alternatives you would recommend. Anything that’s on the high street such as Screwfix or Toolstation then even better. Thanks.
Nope.ChatGPT suggests it’s comparable to MK Toughplug. Any thoughts ?
I meant to ask before .... why do you feel the need for a 'heavy duty' plug?Hi again…Evri have played a blinder and lost my MK Toughplug package. Are there are any other heavy duty alternatives you would recommend. ...