This looks like an Albion Mainsflow(uncased) thermal store.
Thermostat on side should be set to 78 and if you have hot water control on timer it should be on constant.
There were two versions.
One had a primary coil from boiler (sealed system boiler) but these usually never had a pump on primary as the boiler had one in it.
The main store water at 78 degrees also circulated round the rads and the main problem was lack of inhibitor as the store held 200 litres and further 100litres on heating circuit.
Also the primary and boiler in sealed coil would need inhibited separately.
There was a second coil that the domestic water went through.
Major problems were slugged primary coil(slushed on inside and also on outside of coils), cylinder does not get to 78 and boiler cycles as it can't transfer heat to store. So store is too cold, when you put rads on then the store cools down and boiler can't get it back up quickly enough so if you run water it is colder!
Second problem was furred up(on outside) of domestic water coils this leads to a short blast of hot water from coils them almost stone cold water as no transfer from store to coil.
I personally would take it to scrappy and put in a decent unvented cylinder. Just problem of running the blow off from it to outside and ground level from attic!
Thermostat on side should be set to 78 and if you have hot water control on timer it should be on constant.
There were two versions.
One had a primary coil from boiler (sealed system boiler) but these usually never had a pump on primary as the boiler had one in it.
The main store water at 78 degrees also circulated round the rads and the main problem was lack of inhibitor as the store held 200 litres and further 100litres on heating circuit.
Also the primary and boiler in sealed coil would need inhibited separately.
There was a second coil that the domestic water went through.
Major problems were slugged primary coil(slushed on inside and also on outside of coils), cylinder does not get to 78 and boiler cycles as it can't transfer heat to store. So store is too cold, when you put rads on then the store cools down and boiler can't get it back up quickly enough so if you run water it is colder!
Second problem was furred up(on outside) of domestic water coils this leads to a short blast of hot water from coils them almost stone cold water as no transfer from store to coil.
I personally would take it to scrappy and put in a decent unvented cylinder. Just problem of running the blow off from it to outside and ground level from attic!