We've just had a new CU fitted and the electrician who fitted it is stumped.
It's a 15 way box with 4 lighting circuits and freezer running from the main 100mA RCD and the rest running from a 30mA RDC. It's been in a month and initially tripped several times a day or night with no pattern to things in use at the time.
He initially tested the RCD and found it to be faulty and replaced it - it now only trips every 3 or 4 days.
By leaving various circuits off we have fairly confidently identified the problem as being the downstairs power ring. He has identified that this circuit has a lower leakage resistance - still many megohms and legal, but less than the other circuits. I'm not sure that this was enough to cause enough leakage, but we are getting desperate for ideas! We have spent three hours disconnecting each downstairs socket and testing the wiring between each. One length in particular - a spur out to the garage has the lowest resistance so we confidently disconnected that. Today it tripped again, even with this disconnected.
At the time it tripped, nobody was in the house and the only things running were a fridge, satellite and Tivo box (like sky plus) and a couple of computers plus clock radios and such like.
We are stumped. Ideas please?