If it's a TT supply, then PME conditions can not apply, so a 2.5mm² main earth is sufficient providing it is protected against mechanical damage.
If you're running an earthing conductor underground for TT and it is protected against corrosion & mechanical damage, then you can use 2.5mm².
If it's a TT supply, then PME conditions can not apply, so a 2.5mm² main earth is sufficient providing it is protected against mechanical damage.
If you going worst case then the maximum Eli from electricity copanies are
TN_C_S 0.35OHMS
TN-S 0.8OHMS
TT 21OHMS