scotsparky
Before a big argument breaks out thats 21 ohms is the max resistance on the suppliers side of a tt sytem you have to add the 21 on to the installations earth electrode
Just out of curiosity how did this forum subject start????? I forgot as it went on a strange tangent.
Question: What might be a best case likely current to earth on a TT supply caused by a dead short phase to earth?
Let's say best case scenario for Ze: 22 ohms. Highest voltage 252.
252/22 = 11.45A
Sure, I can see your point: there is no harm in using the standard conductor csa's on a TT install. However, you don't have to: you can install a 2.5mm² earthing conductor & 6mm² PE bonding conductors on a TT install and be perfectly compliant.