Simpy put, if you have a 6M UPS2 pump then you will/should have 2 setting modes, one mode, with a solid green LED., which your pump is running on? has 3 different setting settings which should be marked I,II & III on the pump, you can change these settings by pressing the setting button briefly, setting i sets the pump speed to give a maximum head of 4.0M with no flow so your relatively small system will probably result in a head of 3.5M (ish) & a circulation rate of around 8 to 9LPM, setting II gives a max head of 5.0M so ~ 11LPM at 4.7M, setting III is still higher at 6.2M and very rarely required.
The pump will change to its other mode, proportional pressure or PP (mode) if you keep the setting button pressed for 3 to 5 secs and will be incicated by a (the) flashing green LED, this mode also has three settings, there is very littly difference in these settings, setting III, the highest only gives a 3M head with a huge flow rate of 33LPM so will probably only give you around 6LPM at a head of ~ 1.7M.
So suggest running it on fixed speed (solid green LED) on setting I to give ~ 3.5M/9.0LPM or give it a go on PP mode (flashing greed LED) on setting III which may (and only may) be sufficient at ~ 1.7M/6.0LPM