How do I achieve that as boiler goes into standby after few minutes of HW only?Yes, your best bet is to fire the HW only, say a hour or so in the morning before the CH and something the same in the afternoon/evening.
Boiler flow temperature is already at max now.Of course increasing the boiler flow temp to max will give another boost and not cost a fortune in the summer with HW demand only.
The flow is the top one (normal inlet) and return is the bottom one (normal outlet)Say a 10C dT, a bit unusual but the flow may be into the bottom (normal outlet) of the coil and out through the top (normal inlet), that gives a coil output of, 10*60*10/860, 6.98kw, (assuming flowrate @ 10LPM), fairly low, and may account for the boiler having difficulty in getting away and it will certainly cause the boiler to cycle sice the boiler's minimum output is > than the coil output.