It's AutoWhat is the pump setting just now?.
and also look at the s parameters, there may be a clue there.
What/where is the s parameter?
It's AutoWhat is the pump setting just now?.
and also look at the s parameters, there may be a clue there.
If you have a IR gun check the boiler return (and flow) under the boiler and compare them with d.40&d.41 sometime.
Yes, ABV installedIs there a manual bypass or a ABV (automatic bypass) installed anywhere?.
No confusion at all. A high output underfloor heating system will give you about 80 watts heat output per square metre × 85m² = 6.8kW. 8 radiators adds another 8kW (ish) so around 15kW. In reality your UFH is probably running at around 50w/m² unless you have a particularly cold and draughty house, knocking it back to 4kW total, add those radiators on and you're at about 12kW.Apologies for the confusion, 85m² is area that the underfloor heating is covering, I think between 600 to 700m of UFH piping was laid.
Have you been provided with a copy of the calculations?Yes the builders subcontracted the Heat loss calculation to their engineer, I wanted the sensoCOMFORT initially but the engineer dissuaded me with disaster stories like a fool i bought his nonsense
No confusion at all. A high output underfloor heating system will give you about 80 watts heat output per square metre × 85m² = 6.8kW. 8 radiators adds another 8kW (ish) so around 15kW. In reality your UFH is probably running at around 50w/m² unless you have a particularly cold and draughty house, knocking it back to 4kW total, add those radiators on and you're at about 12kW.
So yes, boiler likely to be massively over-sized for the system it's attached to.
Same issue on a 15 year old vaillant. Apparently it is normal, and if your new boiler is doing this then I suppose it is.Your assumption of running for 5 to 10 minutes then cycling is correct. what i don't understand is why during that 5/10 minute period it hovers at 49°C then suddenly shoots up to 70°C but I've changed d.02 to 25 minutes and will monitor this over 24 hours.
My IR gun doesn’t give correct temp when measuring the pipes but seems to be fine for everything else! I’ll pick another one up soon.
Understood, I assumed it was based on amount laid rather than coverage, i'll adjust and continue to monitor through out today.No confusion at all. A high output underfloor heating system will give you about 80 watts heat output per square metre × 85m² = 6.8kW. 8 radiators adds another 8kW (ish) so around 15kW. In reality your UFH is probably running at around 50w/m² unless you have a particularly cold and draughty house, knocking it back to 4kW total, add those radiators on and you're at about 12kW.
So yes, boiler likely to be massively over-sized for the system it's attached to.