We get a house buyers report, this includes electrics, but rather general, mine for this house pointed out a disused fuse box in the void between ceiling and floor, which actually was not disused.
An EICR goes much deeper, it includes things like inspecting some selected sockets and ceiling roses, and also testing. It seems the EICR in this case is no better than the house buyers report, which technically as it includes the electrics could have the label EICR.
There is no laid down rules as to what the EICR includes, it is down to person commissioning the report, so with a buy to let property in England it would want to follow what the new law says, so would not include DNO equipment but would include many items which would normally be inspected and tested as in-service electrical equipment (PAT testing) not part of the EICR.
The LABC can and do instruct inspectors to list all items not complying with current edition of BS 7671, this is because it replaces the installation certificate, again the LABC is the client so they can instruct as to what they want.
However unless special instructions the normal is to follow the
Electrical Safety Council best practice guide 4 issue 5 I don't agree with all it says, but it is still a good guide. The IET also do
Model forms it does seem odd when the IET dropped code 4 that they then produce a model form with all the regulation numbers listed, however if we take 6.6 as an example "Suitability of equipment for external influences for installed location in terms of IP rating (701.512.2)" going to the regulations tells one if IPX7, IPX5 or IPX4 is required, so it is more of a guide for the inspector than for the client so he can see if it complies.
If not potentially dangerous does it matter? Well the answer is yes, if you for example want to add sockets, you need to know before you add sockets a RCD will need installing, however as said code 4 was removed, so no point making code C3 into a code 4.
In the main the model form is a check list for the inspector, but I do note worded so same item not listed twice "Presence of supplementary bonding conductors, unless not required by BS 7671:2018 (701.415.2)" note unless not required and 701.415.2 does say "Where the location containing a bath or shower is in a building with a protective equipotential bonding system in accordance with Regulation 411.3.1.2, supplementary equipotential bonding may be omitted where all of the following conditions are met:" as part of it.
But the report shown looks more like a house buyers report to an EICR, written by some one who has no idea that a SPD for example is not required in domestic premises. So I would file here
or what ever your waste paper bin looks like. And if you commissioned it ask for a refund.